Mike Casey avatar image
Mike Casey asked
BYD LVL 15.4 (120kWh) - I want to increase rate of charge and discharge
Right now I have the following setup
CVL 58.4V
CCL 1944A
DCL 1994A
However when I set grid point to 100kW or -100kW the most the batteries seem to want to take and give is around 60kW.
Im just wondering if I am missing something, as with those figures I would be expecting well over 110kW i/o
Thanks,
Mike
BYDcharge current limit
Hi Mike,
There are several other factors that might influence how much power you are able to charge and discharge.
Some other factors that need to be considered:
What inverters are you using?
The accounting for the kVA to kW differential, and temperature (these are listed in the inverter spec sheet)
The AC input current limit
The grid voltage
100 kW is a significant amount of power, It would be a good idea to discuss this directly with the Victron agent who sold you the system. There may be other limitations as well.
Victron BYD battery compatibility guide