question

akofler avatar image
akofler asked

ESS PV Inverter ac-input not charging battery

Dear all,

I have:
- Multiplus-II 48/8000 v494
- LiFEPO4, Orion BMS via Can, 48V
- PV Inverter parallel to ac-input
- Energy meter EM24 on PV inverter, configured as PV-Inverter
- Cerbo GX v2.84
- ESS & DVCC enabled
- Scheduling charge disabled

Setting up in ESS the mode with or without BatteryLife the charge power is going from 0- 100W, not more, even there is excess PV power:

1647249721381.png

Setting the ESS mode to Keep Battery charges, the charger charges well with the maximum current.

Why are there no dots from the PV Inverter to the Multiplus ? It seems that for some reason / missconfiguraion the excess power is not calculated well.

It seems that the Consumption is almost as high as the PV production.


Do you have any suggestions ?

Many thanks

Andreas



Some config Screenshots:

1647249997241.png

1647249925069.png1647249916623.png1647249847706.png

1647249899078.png

1647249941545.png

1647250050266.png


AC PV Coupling
1647249721381.png (28.8 KiB)
1647249847706.png (33.2 KiB)
1647249899078.png (33.7 KiB)
1647249916623.png (30.4 KiB)
1647249925069.png (23.9 KiB)
1647249941545.png (13.1 KiB)
1647249997241.png (25.0 KiB)
1647250050266.png (29.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
markus avatar image
markus answered ·
You will need an additional grid meter for the PV inverter on AC-in to work.
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

akofler avatar image akofler commented ·

Dear Markus, sadly the connection PV/Grid is inside a sealed chassis, so i can't install a grid meter. But anyway, Is the option Grid Metering --> Inverter Charger not enogh ?


1647257461973.png


0 Likes 0 ·
1647257461973.png (34.5 KiB)
markus avatar image markus ♦♦ akofler commented ·

Unfortunately, to bring the ESS system to charge from the PV-inverter on AC-in, you would have to reconfigure the system to have 2 energy meters, one measuring PV and one measuring grid.

like this:

1647259809472.png

0 Likes 0 ·
1647259809472.png (38.7 KiB)
akofler avatar image akofler markus ♦♦ commented ·

Sadly this point isn't accessible due the seal.

Since all loads are connected to AC out1 the calculation of the power is simple: P_grid = P_pv + P_ac_in_multiplus

Is there a way to implement on the Cerbo a kind of virtual sensor doing this simple calculation (i.e. script reading / writing D-Bus running on Cerbo) ?

Is this information available on the D-Bus ?

Thanks


0 Likes 0 ·
markus avatar image markus ♦♦ akofler commented ·

You could ask here in Modifications space, if someone has a solution. Official anwer will most probably be „no“


https://community.victronenergy.com/spaces/31/index.html

0 Likes 0 ·
akofler avatar image akofler markus ♦♦ commented ·

ok thanks a lot !

0 Likes 0 ·
akofler avatar image akofler markus ♦♦ commented ·
Hi Markus, I've just enabled the ssh service to the Cerbo, so I can check

the exported Items on thd DBus. Which Items hsa to be set to get the ESS working with an AC Inverter connected to the input ?

Thanks

0 Likes 0 ·
markus avatar image markus ♦♦ akofler commented ·

Hi,

I don't know.

Alternatively, you could control your ESS via ModbusTCP. This is maybe the better approach: ESS mode 2 and 3 [Victron Energy]