matt1309 avatar image
matt1309 asked
Victron multiplus sizing/max throughput
I've seen some conflicting threads on the below question.
What is the max load I can attach to multiplus ii 5000Va? Assuming I have grid attached 24/7.
AC-in notes 50amp input (aka max 230*50 = 11,500W)
What loads can multiplus ii output for this model. Manuals seems to say the below option 1 below assuming grid is connected all the time.
1. Is it 50amps (11,500w) from ac-in plus the inverter element 5kva (5000/230 = 22amp) being total output circ: 72amps (16500watts)
Or
2. Is 50amps total (11,500w)
Or
3. 22amps (5000w)
I understand if grid goes down then inverter can only output 5kva option 3 but I'm more curious as to what the peak output is.
I think I'm confusing pass through vs power assist.
I'm trying to size a multiplus/quattro for peak loads of 16000Watts
Thanks,
Matt
Multiplus-IIpeak
wkirby avatar image
wkirby answered ·
It is 50A + 22A for 72A maximum output current.
The 50A limit is for the AC-IN, maximum current for the backfeed relays.
The manual gives an example for the 3kVA version:
With its PowerAssist feature the Multi can add up to 3 kVA (that is 3000 / 230 = 13 A) to the output during periods of peak power requirement. Together with a maximum input current of 32 A this means that the output can supply up to 32 + 13 = 45 A.
Page 10 of the manual here:
https://www.victronenergy.com/upload/documents/Manual-MultiPlus-II-12V-24V-48V-3k,-5k,-8k,-10k-230V-EN-NL-FR-DE-FI-SV.pdf
matt1309 avatar image matt1309 commented ·
Thanks very much for confirming. I did spot that in the manual but saw some threads that said otherwise.
Thanks, Matt
rob-in avatar image rob-in commented ·
The manual doesn't actually state that 3kVA addition is related to any specific model. It could be interpreted as there being a 3kVA addition for every model! This would be illogical but needs clarification, I have asked about that today in a new question.
Alexandra avatar image Alexandra ♦ rob-in commented ·
The post is old. The manual at this time was written for the 3kVa.