Victron Multiplus II GX, Modbus-TCP register restart after ~1min

Good morning,

After changing register 37, 40 or 41 in com.victronenergy.vebus, the charge/discharge will stop after approx 1 to 2 minutes, while value on the registers stay the same.

ESS mode is on External Control. Other registers were checked for potential blockage/wrong value yet everything seems to be ok.

What could be the problem?

Modbus TCPvictron products
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
tnt369 avatar image
tnt369 answered ·

These register (37...) need to be writen every minute (or more often) to show the multiplus that the external control is still alive.