lala avatar image
lala asked
Pylontech Force L1 High discharge current alarm on low Load
Good day,
I have from a Pylontech Force L1 with 21kWh with 6 modules.
I have a Victron Multiplus II 5000-48 with a limit of 3000W as a grid-tied home storage. Again and again when the memory is relatively full, the memory brings a discharge protection. Even with low withdrawals. Most of the time the error disappears by itself. But every now and then I unfortunately have to turn the Force L1 off and on again, but that is not a solution. The system is from August 21. Do you have any idea what this can be?
In the attachment are a few pictures.screenshot-20220222-120426-chrome.pngscreenshot-20220222-120436-chrome.png
The battery alarm comes from the internal shutdown of the Force 1.screenshot-20220222-162717-chrome.pngscreenshot-20220222-162840-chrome.pngscreenshot-20220222-162820-chrome.pngscreenshot-20220222-162750-chrome.pngscreenshot-20220222-162756-chrome.pngscreenshot-20220222-162742-chrome.pngscreenshot-20220222-162706-chrome.png
Ausgelöst durch Beschreibung Gestartet bei Gelöscht nach
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 16:40:13 30s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 16:22:34 26s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 16:10:47 2m, 52s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 14:44:43 22s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 14:44:21 3s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 14:44:14 5s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 14:40:03 10s
Battery Monitor - PylontechForceL1 21kWh [512] Automatic monitoring High discharge current alarm: Alarm 2022-02-22 14:40:00 2h, 23m, 58s
Battery Monitor - PylontechForceL1 21kWh [512] Automatic monitoring High discharge current alarm: Alarm 2022-02-22 14:35:35 1m, 49s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 14:31:53 29s
Battery Monitor - PylontechForceL1 21kWh [512] Automatic monitoring High discharge current alarm: Alarm 2022-02-22 14:31:50 1m, 2s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 11:20:18 49s
VE.Bus System [276] Automatic monitoring Low battery: Alarm 2022-02-22 11:20:04 3s
Battery Monitor - PylontechForceL1 21kWh [512] Automatic monitoring High discharge current alarm: Alarm 2022-02-22 11:20:04 1m, 2s
Multiplus-IIESSPylontech
lala avatar image
lala answered ·
An update of the Pylontech firmware via the manufacturer solved the problem.
@lala
Glad it was resolved.
Thank you for coming back and sharing the solution that worked for you.
Jan Zmrhala avatar image Jan Zmrhala commented ·
What is the updatw process? Can I do it online?
laulau avatar image
laulau answered ·
hi,
how did you do the update? I can't connect via rs232