bryn asked

generator choices offgrid

I am about to change our inverter over to a new victron, and we need to get a generator to go with it.


The system will be a venus GX and a victron multiplus 5000/48 AC-coupled with a fronius primo 5-0-1 and later on a DC coupled blue solar MPPT. Batteries are 2x LG RESU 10, so 20kwh in total.


I want the AC input on the multiplus to be a generator- for charging only. I've always been told that we need to use an inverter generator to keep the power quality up but I note that a few places on the victron site suggest that AVR units will be fine- thoughts? I don't want a huge generator, about 5kva ish is my plan, and use the current limiter on the ac input to ensure its not overloaded.

Generatoroffgrid
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

daniel1957 avatar image daniel1957 commented ยท

inverter generators are notoriously unreliable so just go for a 50hz (60hz) 4 pole 1500 RPM (1800) diesel.

Do not use a 3000 RPM (3600) !

1 Like 1 ยท
9 Answers
boekel avatar image
boekel answered ยท
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ian avatar image
ian answered ยท

An SDMO in the 6 to 10 Kva range would be a nice choice

LG Resu are not a good choice for off grid set-ups however. 2 x BYD B-Box or B-Box pro would be better, or Victron home brand Li Fe PO4

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

bryn avatar image
bryn answered ยท

batteries already exist- we have an existing system where the inverter is not coping, so I need to swap it out.


that multiplus page is what I was referring to- it says AVR units are ok. I guess I just want to validate that people find they do work ok and that I don't need an inverter unit.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

JohnC avatar image
JohnC answered ยท

Hi Bryn. I don't think Victron have any particular recommended types (at least officially), and they've put some work into testing them (perhaps before the inverter era). This is ageing a little now, and it's quite lengthy, but you may have your eyes widened if you delve to the more technical aspects: https://www.victronenergy.com/upload/documents/VE_Marine_generator_test_RVA_07-jan-2008.pdf

I've a 48/5000 Multi at home and have used both types. The Multi is fairly picky about power quality and my old Yamaha AVR it doesn't like. But can be tweaked to accept it, with some loss of power capacity and efficiency.

If you could find a supplier to 'guarantee' acceptance by the Multi, then go for it.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

christyler avatar image
christyler answered ยท

I use a Cummins Onan 4.8 me, it works really well, and it's easy to integrate the remote start

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Andrew Jefferies avatar image
Andrew Jefferies answered ยท

I run a Kubota 1105BG close coupled to a Mecc Alte (manual switching 1ph/3ph) 230/415Vac Alternator . AVR is digital, rock solid. Power quality is very good. 49-52Hz, 6kVA cont, 9kVA int', runs at 3.3 kW for 3hrs / day now that I have upgraded to Lithium. 2x Multiplus 3000's(parallel) set for 32A input current limit. Murphy Auto-Start. Engine coolant is fed through heat exchanger and provides ALL of my DHW + some house radiators. Its all over 15 years old now, just regularly serviced replaced the water pump once.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

alan avatar image
alan answered ยท

Get something with a high quality Digital AVR, I've set up multiple now with Westinghouse AVR units and at all of the sites the multiplus accepted power with UPS enabled.
I've also seen kubota lowboy GL9000's work with UPS ticked.


I've seen cheap sabre generators need UPS switched off, as well as a couple of 1500rpm kubota's (these were rebuilt units so god only knows what the Alternator was)


The westinghouses with the wave flow muffler are quiet for what they are.


Bottom line, don't go cheapest. Fuel type is going to be a deciding factor.

For a 5kva multi, you want something in the 6.5kva continuous output.

Don't get an inverter unit, sure they can work with current limit, but after running at close to its rated load for for a few hours the inverter in the unit will overheat but the engine will keep going and you won't know if you don't hear the rev change.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pauldeegan avatar image
pauldeegan answered ยท

Does anyone have any suggestions for a 10 - 14kVA diesel generator that works well without "Weak AC" selected?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nesswill avatar image
nesswill answered ยท
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pauldeegan avatar image pauldeegan commented ยท
Can you confirm that you can operate these generators with "Weak AC" selected OFF?