offroadflow avatar image
offroadflow asked
Vast difference of solar input power and inverter output power
3x 48/5000 Multi
2x 250/100 MPPT
Venus GX
Batteries in IDLE mode.
No DC consumption at all (off grid installation).
Solar in/power out has a difference of about 800W.
This can't be right..?
A few hundred watts in energy loss OK, but 800??? This gap is constant, even getting bigger with more power out (through)..
MPPT Controllerspower meter
nickdb avatar image
nickdb answered ·
Depending on the type of load, inverted resistive loads lose about 10% at the most efficient, other load types lose more.
Reporting isn't always in sync, at 13% that is about right for efficiency.
It's basic physics.
seb71 avatar image
seb71 answered ·
Maximum efficency of your inverters is about 95%. The efficiency drops at higher loads.
Also each inverter draws 20W or so for self-consumption. The MPPTs have some small power draw. Venus GX probably takes 5W or so. Cable/wire loses can be high, too, if the wires are undersized. After you take these out, you are left with about 89% overall efficiency. Not great, not terrible. :)