Using ATS between Grid & Generator at AC IN

Is it safe to use two inputs ( Grid and generator ) connected to an automatic transfer switch in this manner as shown in the image below ?
Does the easysolar II gx accept voltage that might not be stable coming from the generator ?

screen-shot-2021-10-26-at-65831-pm.png

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

Yes, there should be no problem using an ATS on the AC input like this. The Inverter setup includes a check box for weak ac input, and some other parameters may need adjustment depending on your generator.