Losing Amps??

Hello,

I have an off grid fixed system with no AC in, connected to 4 battleborne batteries in parallel to a Lynx Power In. Its about 9 feet (2 feet using 2 AWG to Lynx then 7 feet much thicker 4/0 AWG) from the actual batteries to a Multiplus 12/3000/120.

When I look at the display for the inverter inside VictronConnect software app under "current" for the AC OUT it will display around 1amp, but under battery "current" it will say from 5-7amps.

Is this actual loss? And if so is that a normal loss rate?

I have networked my MPPT, shunt, and inverter. And I'm pretty sure all my settings are correct BattleBorne guided me through it.

Multiplus-IIamps
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

P = U x I

Higher voltage -> lower current for the same power

Lower voltage -> higher current for the same power

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mikedonner avatar image mikedonner commented ·
ah yes, thank you