EM24 and two inverters

Hello fine people!

I currently have a Multiplus II and an EM24 that is setup as an inverter.

I'm planning to install a second installation. The question is if I can add this installation also on the EM24?

em24
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
chuff avatar image
chuff answered ·

Yes, you can as 6 tcp client can use the EM24 but there are some instability is this type of configuration and sometime the EM24 block itself wihtout sending any data more. I have this configuration in test since four month, good for a labo bit not in production.