The Cerbo GX manual says to use a 1A fuse, but the Fuse that came with the unit is rated at 3.15A (model written on the Fuse: F. T3.15A E250V P).
What is the correct replacement fuse I should purchase?
Thanks!
The difference between a 1 A and 3 A fuse is negliable from a safety perspective. But the 3 A is superior, it has less resistance, less voltage drop, and more tolerance for a less than perfect connection, so itโs better to use it, but 1A will still work.
In this case when there is a current limited supply, it is less important, but I would never say a fuse is pointless, its purpose is in the event of a fault.
The correct fuse size is 3.15 Amp.
There was a mistake in the original manual, it has since been corrected in the master and should be published Monday.
Did the supplied fuse blow somehow?
Thank you for the information Guy... and thanks for the private email as well!
The "slow blow" part in the manual was correct, right? So 3.15A Slow blow fuse?
BTW, no, the fuse is not blown. Since this is on a boat that is often away from shore, I always like to have spares on hand! :-)
Slow blow is better if you can find it. But a fast blow will also be acceptable as a substitute if necessary.
The system schematic downloads (on the victronenergy.com site) that feature the Lynx BMS all show the Cerbo being powered from the Lynxโs AUX port via a 1A fuse.
Further, the Lynx BMS manual states โIt is recommended that the system includes a GX device powered by the AUX port.โ.
The maximum continuous current rating of the AUX port is 1.1A according to the Lynx BMS manual (several places).
Two questions.
13 People are following this question.