Quattro 48/3000/35 120 v

I have both a 220V and 120V Inverter on my boat. On the Color Control Panel 'Tiles' it is defaulting to the 120 even though the power is solely through the 220 inverter/charger here at the dock. How do I get the 220 Quattro to show up on the Color Control panel - and when I am at a 120 dock how do I get it to show up then?

CCGX Color Control
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
nickdb avatar image
nickdb answered ·

You can't connect two independent inverters (even if they are sharing a battery) to one GX. It will only use one of them. That is how the system is designed.

Yes you can physically connect them but one will always be ignored, by design.

It is an unusual config, you will need to disconnect whichever one you are not planning to use or get another GX.