question

pelements avatar image
pelements asked

Venus OS 3.20 MQTT Ac Setpoint BUG

Hello ,

Since Update 3.20 I have a Problem to write AcPowerSetpoint per MQTT...

If I write a Positive Number, all works fine but if need to send a Negative Number the MQTT Broker doesn't take the Number ...All other Values work fine ..( max inverter power ,Enable Charge ,Enable discharge )

Control over Modbus TCP works fine ...


System Aufbau

3x 15000 Quattro 48/15000/200-2x100

1x Cerbo GX

ESS run on external Control , the Cerbo GX is controlled of ah industrial Raspberry PI with Node-Red.Each phase is regulated individually

 
                


firmware update
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
mvader (Victron Energy) avatar image
mvader (Victron Energy) answered ·

Hey!

Fixed per beta v3.30~6.


Thank you for reporting! The clear reports helped fix this so quickly.

And apologies for that bug.

We’ll release this fix in an official release, ie v3.21, next week or the week thereafter.

Meanwhile, either run v3.14 official, or a v3.30-beta.


Have a good evening, Matthijs