question

mike1234 avatar image
mike1234 asked

Cable Size Mulitplus 2 12v 240v

I am planning the wiring for a Multiplus 2 12v 240v inverter. The manual states 2 x 50mm2 cables for both the positive and negative and a 400A mega fuse. Given that the max rating of a 50mm2 cable is 345A could two cable be run as per the pic at 50mm2?Inverter Wiring.pdf

rj45 cable
inverter-wiring.pdf (62.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

5 Answers
the-doon avatar image
the-doon answered ·

Where are you finding 345A? I use the orange welding flex which is about as good as you can get and 50mm is rated to 217A.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

the-doon avatar image
the-doon answered ·

Here is the data sheet I useimg-5599.png


img-5599.png (580.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

the-doon avatar image
the-doon answered ·

0B&S is 246Aimg-5602.png


img-5602.png (325.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mike1234 avatar image
mike1234 answered ·

Maybe I misunderstood but this is the guidance I looked at

1706083099167.png


1706083099167.png (66.6 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

the-doon avatar image the-doon commented ·
Very interesting. That’s a huge difference.
0 Likes 0 ·
kevgermany avatar image
kevgermany answered ·

Go with the Victron manual specs. Although different cable types have different ratings for the same size, what's missing here is resistance and operating temperature, as well as how the cables are installed.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources