There seems to be an internal fuse in the easy solar, as it is shown in the manual, but I don't know if this protects also the cable from /to the batteries and even not what size it is.
There seems to be an internal fuse in the easy solar, as it is shown in the manual, but I don't know if this protects also the cable from /to the batteries and even not what size it is.
Incide the easy solar, there is one fuse to protect the inverter/charger, and another fuse inside the MPPT unit. So depending on the length of your cables to the battery (<2m), you could avoid the external fuse.
Thank you for your fast response. I'm planning some DC loads direct from the batterie. This is why I think about an external fuse, too.
But the fuses in the EasySolar will not protect the cables if there's a short. The BMS might, depends on that model.
You should really have a battery isolator at or close to the battery positive terminal. Maybe use a suitable circuit breaker which will act as fuse and isolator. But avoid the cheap ones. They have a reputation for unreliability and inaccuracy. From there wire to easysolar and a fused distribution box for the loads.
OK: IF the battery cables are "short" (in length) then a single fuse can protect the cable and the battery. As mentioned above, an isolator should be included for ease of service. HOWEVER: If the battery cables are "long" (>3m) go through a wall or other barrier, then there is a chance that the cables may be damaged and short to each other. To protect this, a fuse / Disconnector is ALSO required at the battery.
Large battery banks also require segmentation fusing / isolation in order to keep "ARC Flash" energies in safe areas.
44 People are following this question.