I thought I would share a little project I have been working on.

I have made a simple WiFi temperature sensor using an Arduino. The Arduino sends the data to a Venus GX device using MQTT and Victron's dbus-mqtt. I wrote a simple device driver (based on the dummyservice.py) to register the device with dbus so that the data it sends is displayed on the GX device screen and is sent to VRM. In this way it was quite easy to piggy back on the new Ruuvi support in the dbus.

I plan to have a few of these Arduino mqtt sensors on my boat and each Arduino will probably end up with multiple sensors in addition to temperature. I decided that writing and deploying a separate device driver for each one was not a great solution. So I have written a generic dbus-mqtt device driver that will allow multiple MQTT based sensing devices to self register to the dbus, then publish data for multiple dbus services and subsequently send that data over the existing Victron dbs-mqtt api. This will make creating new MQTT based sensors much easier as no extra drivers will be required.

screenshot-2022-02-19-at-211151.png

screenshot-2022-02-19-at-210939.png


If anyone is interested in learning more or trying it out for themselves, please go to https://github.com/freakent/dbus-mqtt-devices..

Be sure to read the README for details of the registration protocol.

My Arduino project is also available at https://github.com/freakent/mqtt_wifi_sis but this is still work-in-progress.

Temperature Sensor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

37 Answers
gone-sailing avatar image
gone-sailing answered ·

Quick update, I added support for Tank level sensors. I have run some simulated tests and all is looking like it works OK with both temperature and tank sensors.

1645723079289.png


I'm running a demo mode on the Venus device and getting some DeviceInstance number overlaps with demo devices. Hopefully that is just a quirk of the demo mode not registering devices correctly with the dbus. When I get some time I'll look into hooking up a tank level sensor to my Arduino.

The updated driver can be found on my github page: https://github.com/freakent/dbus-mqtt-devices



1645723079289.png (38.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Hi,
thank you very much for your work and the documentation on github.
I will try to replicate it with a Tasmota or espEasy device.
My goal is to register a Sonoff device via MQTT as PV inverter.
Best regards,
Sebastian

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marv21 avatar image marv21 commented ·
1 Like 1 ·
gone-sailing avatar image
gone-sailing answered ·

Hi StundenBlume, Have you figured out which paths on the dbus you would need to push values to for your use case?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Hi,
first I will to follow your example. Than I will look into that.
But before all that I have to figure out why my venusOS don't recognize my Pylontech battery.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

here is my experience: Installation without problem but I didn't get it to work.
What I did:

  • Install like you documented, no problem
  • reboot
  • connected to venusOS with MQTT client id "b815"
  • subscribed to "device/#"
  • published to "device/b815/Status" payload "{ "clientid": "b815", "connected": 1, "version": "v1.0 ALPHA", "services": {"t1": "temperature"} }"
  • no response under "device/#", don't get the "DeviceInstance message"
  • published to "device/b815/DeviceInstance" Payload "{"t1": 5}"

I expected to see "W/<portal id>/temperature/<device instance>/Temperature" to show up.

Did I messed something up?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Hi Stundenblume, thanks for trying it out and giving feedback.

First thing to check is that the dbus-mqtt-devices service is running, from the ssh command line use

$ svstat /service/dbus-mqtt-devices


if the service is running, then next thing to check is the log with the command:

$ more /var/log/dbus-mqtt-devices/current

It should contain something like this:

@400000006238ead134c233e4 INFO:device_manager:Received device status message {'clientId': 'fe001', 'connected': 1, 'version': 'v1.0', 'services': {'t1': 'temperature'}}
@400000006238ead134c25324 INFO:device:**** Registering device: fe001, services: {'t1': 'temperature'} ****
@400000006238ead134c25edc INFO:device:Registering Service temperature for client fe001
@400000006238ead134c26a94 INFO:device_service_config:About to open config file
@400000006238ead136d95fcc INFO:device_service:Unregistered mqtt_fe001_t1 from dbus
@400000006238ead136df10d4 INFO:device_service:Unregistered mqtt_fe001_t1 from dbus
@400000006238ead136ea9ddc INFO:device_service:Unregistered mqtt_fe001_t1 from dbus
@400000006238ead13755bbbc INFO:device_service:Registering service temperature for client fe001 at path com.victronenergy.temperature.mqtt_fe001_t1
@400000006238ead13903b20c INFO:settingsdevice:Setting /Settings/Devices/mqtt_fe001_t1/ClassAndVrmInstance does not exist yet or must be adjusted
@400000006238ead13a94dd44 INFO:vedbus:registered ourselves on D-Bus as com.victronenergy.temperature.mqtt_fe001_t1
@400000006238ead13ac572c4 INFO:device_service:Registered Service com.victronenergy.temperature.mqtt_fe001_t1 under DeviceInstance 1
@400000006238ead13ad8d79c INFO:device_manager:publish {'t1': '1'} to device/fe001/DeviceInstance, status is 0


If you can have ssh open in another window, then

$ tail -f /var/log/dbus-mqtt-devices/current 

is a useful way to monitor the driver


I highly recommend using MQTT-Explorer to monitor the queues while debugging and if you are doing anything with MQTT.

http://mqtt-explorer.com/


Finally, if you have re-installed more than once, make sure there is only one line in your rc.local for dbus-mqtt-devices.

$ more /data/rc.local 

edit: for anyone else reading this, please also make sure that /data/rc.local is executable with

$ chmod +x /data/rc.local
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dafyddhirst avatar image dafyddhirst commented ·

Just a try on some versions rc.local is not executable

chmod +x /data/rc.local

reboot


0 Likes 0 ·
gone-sailing avatar image gone-sailing dafyddhirst commented ·
Good point! I will add that to my set up script. Thanks.
0 Likes 0 ·
stundenblume avatar image
stundenblume answered ·

thanks for you recommendation "mqtt-explorer" a very nice software and a lot more suitable than the mqtt-box extension for chrome.

$ svstat /service/dbus-mqtt-devices

gives me

/service/dbus-mqtt-devices: unable to chdir: file does not exist


$ more /data/rc.local

gives me

ln -s /data/drivers/dbus-mqtt-devices-0.2.1/bin/service /service/dbus-mqtt-devices

It looks like rc.local is not executed.


after

$ ln -s /data/drivers/dbus-mqtt-devices-0.2.1/bin/service /service/dbus-mqtt-devices

I get from

$ svstat /service/dbus-mqtt-devices
/service/dbus-mqtt: up (pid 1407) 83405 seconds, normally down


$ more /var/log/dbus-mqtt-devices/current

gives me than

@40000000623b94c31d1c2024 *** starting dbus-mqtt-devices ***
@40000000623b94c50d69c4ec -------- dbus_mqtt_devices, v0.10 is starting up --------
@40000000623b94c50d69e044 INFO:logger:Loglevel set to INFO
@40000000623b94c50da15b64 INFO:mqtt_gobject_bridge:[Init] Connecting to local broker
@40000000623b94c50fbacd54 INFO:device_manager:[Connected] Result code 0
@40000000623b976917ae010c *** CCGX booted (0) ***
@40000000623cdd411a882ed4 *** starting dbus-mqtt-devices ***
@40000000623cdd4308321f24 -------- dbus_mqtt_devices, v0.10 is starting up --------
@40000000623cdd4308323694 INFO:logger:Loglevel set to INFO
@40000000623cdd4308665e24 INFO:mqtt_gobject_bridge:[Init] Connecting to local broker
@40000000623cdd430b0cae94 INFO:device_manager:[Connected] Result code 0

after connecting to MQTT with client id

b815

and publishing

{ "clientid": "b815", "connected": 1, "version": "v1.0 ALPHA", "services": {"t1": "temperature"} }

to

device/b815/Status

I can see with

$ tail -f /var/log/dbus-mqtt-devices/current
@40000000623ce73705437efc INFO:device_manager:Received device status message {'clientid': 'b815', 'connected': 1, 'version': 'v1.0 ALPHA', 'services': {'t1': 'temperature'}}
@40000000623ce737071d6f1c *** starting dbus-mqtt-devices ***
@40000000623ce738327fe8ec -------- dbus_mqtt_devices, v0.10 is starting up --------
@40000000623ce73832800444 INFO:logger:Loglevel set to INFO
@40000000623ce73832af1324 INFO:mqtt_gobject_bridge:[Init] Connecting to local broker
@40000000623ce73834ff3ce4 INFO:device_manager:[Connected] Result code 0

but don't get a device instance.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Hi StundenBlume, Have you figured out which paths on the dbus you would need to push values to for your use case?

If I use a EM24 as 1 phase pvinverter it looks like this:

1648159600806.pngHope this is helpful.

I don't know what the minimal information is to work properly.


1648159600806.png (75.2 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Yes, as dafyddhirst pointed out, the /data/rc.local file does need to be set to executable with a
chmod +x /data/rc.local

Then when you reboot dbus-mqtt-devices will autostart. Without this the links will be wiped by Venus on reboot.

I just noticed that you used my fe001 clientid in the payload, so the registration response would have been published to

  1. device/fe001/DeviceInstance


The MQTT clientid is not as important as the one in the payload.

You should see the registration request being processed in the in the log file.


edit: I origially wrote deviceid when I meant clientid and Status when I meant DeviceInstance, corrected both now.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Looking at the screen shot of the MQTT queues you just posted, I am not sure you actually need my device driver. The device you want to update is already in the dbus under device id 41. Assuming those properties are writable, you should just be able to publish messages to the relevant write topic. You can test that using MQTT explorer.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Sorry I can't figure out how to probably quote here.

I used my device id, that was a copy/paste problem just here. You can see the correct device id in the log file.

I don't see the registration request being processed in the in the log file.

This is all I get

root@raspberrypi2:~# tail -f /var/log/dbus-mqtt-devices/current
@40000000623ce6492d7eef3c INFO:logger:Loglevel set to INFO
@40000000623ce6492db0ec1c INFO:mqtt_gobject_bridge:[Init] Connecting to local broker
@40000000623ce649302af49c INFO:device_manager:[Connected] Result code 0
@40000000623ce73705437efc INFO:device_manager:Received device status message {'clientid': 'b815', 'connected': 1, 'version': 'v1.0 ALPHA', 'services': {'t1': 'temperature'}}
@40000000623ce737071d6f1c *** starting dbus-mqtt-devices ***
@40000000623ce738327fe8ec -------- dbus_mqtt_devices, v0.10 is starting up --------
@40000000623ce73832800444 INFO:logger:Loglevel set to INFO
@40000000623ce73832af1324 INFO:mqtt_gobject_bridge:[Init] Connecting to local broker
@40000000623ce73834ff3ce4 INFO:device_manager:[Connected] Result code 0
@40000000623ce98d1ceb3c84 *** CCGX booted (0) ***


For the pvinverter
This EM24 is just borrowed from someone. I think it would be nice to implement a own pvinverter without adding a original one first.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Unfortunately it looks like it is crashing. We see message saying "received device status message" immediately followed by a line saying "starting dbus-mqtt-devices". I think that is daemontools automatically restarting the service after a crash.

I'll run some tests using your data and see which log files might contain the error from the crash. I am launching my boat tomorrow so I will be tied up with that for a couple of days.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

I just noticed a small but important difference:
{ 'clientid': 'b815', 'connected': 1, 'version': 'v1.0ALPHA', 'services': { 't1': 'temperature'}}

it should be clientId not clientid (uppercase i)

I should put some better validation in the code.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Good morning,
thank you, with "clientId" it works like expected. I copied the line from github.
Look like good weather to spend some time with the boat!
Best regards,
Sebastian :)


1648189475029.png



1648189475029.png (19.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Awesome. Thanks for letting me know.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

I will try to add a pvinverter by editing services.yml

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Until now I didn't tray to to modify your services.yml.

I tried some other things:
1. writing to an existing EM24, defined as pvinverter

W/.../pvinverter/41/CustomName {"value": "test"}

works.

2. writing to

W/.../pvinverter/41/Ac/L1/Power {"value": 1}

or

W/.../pvinverter/41/Ac/L1/Current {"value": 1}

does not work.

So I think it's not writable.


Further I found this information from Victron:

com.victronenergy.pvinverter

/Ac/Energy/Forward     <- kWh  - Total produced energy over all phases
/Ac/Power              <- W    - Total power of all phases, preferably real power
/Ac/L1/Current         <- A AC
/Ac/L1/Energy/Forward  <- kWh
/Ac/L1/Power           <- W
/Ac/L1/Voltage         <- V AC
/Ac/L2/*               <- same as L1
/Ac/L3/*               <- same as L1

/Ac/Current            <- A AC - Deprecated
/Ac/Voltage            <- V AC - Deprecated

/Ac/MaxPower           <- Max rated power (in Watts) of the inverter
/Ac/PowerLimit         <- Used by the Fronius Zero-feedin feature, see ESS manual.
                          Path must be invalid or non-existent for PV Inverters
                          that do not implement Zero Feed-in power control.

/ErrorCode             <- 0=No Error
/FroniusDeviceType     <- Fronius specific product id list
/Position              <- 0=AC input 1; 1=AC output; 2=AC input 2
/StatusCode            <- 0=Startup 0; 1=Startup 1; 2=Startup 2; 3=Startup
                          3; 4=Startup 4; 5=Startup 5; 6=Startup 6; 7=Running;
                          8=Standby; 9=Boot loading; 10=Error


I wrote a python script which wrote to all topics, but without success.
So I think I don't understand how to add a new pvinverter to the victron system.

I will try to understand how you did it with the temperatur and tank sensors.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image gone-sailing commented ·

You could check the file /opt/victronenergy/dbus-modbustcp/attributes.csv to see if the parameters you want to use are set to read or write (last field in the csv).

Feel free to send me your services.yml file and I’ll see how it looks on my test system. Probably easiest to open an issue on the GitHub project and upload it there.

0 Likes 0 ·
stundenblume avatar image
stundenblume answered ·

I got a little farther.

I added the following to services.yml

pvinverter:
  CustomName:
    default: "My PV Inverter"
    persist: true
  ErrorCode:
    description: "0=No Error"
    persist: true
    default: 0
    min: 0
    max: 1
  Position:
    description: "0=AC input 1; 1=AC output; 2=AC input 2"
    persist: true
    default: 0
    min: 0
    max: 2
  StatusCode:
    description: "0=Startup 0; 1=Startup 1; 2=Startup 2; 3=Startup 3; 4=Startup 4; 5=Startup 5; 6=Startup 6; 7=Running; 8=Standby; 9=Boot loading; 10=Error"
    persist: true
    default: 7
    min: 0
    max: 10

When I write to

device/a04/Status { "clientId": "a04", "connected": 1, "version": "v2.3", "services": {"pv1": "pvinverter"} }

Partial success: A new pvinverter is created.

But I don't know how to add "subcategories" like

/Ac/Power

If I add the following to services.yml

  Ac:
    Power:
      description: "W"

I get:

1648556007107.png
Any hint how to get the expected structure?

1648556007107.png (32.9 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·
Ac/Power:

did the trick.

services.yml now looks like this:


[...]

pvinverter:
  CustomName:
    default: "My PV Inverter"
    persist: true
  ErrorCode:
    description: "0=No Error"
    persist: true
    default: 0
    min: 0
    max: 1
  Position:
    description: "0=AC input 1; 1=AC output; 2=AC input 2"
    persist: true
    default: 0
    min: 0
    max: 2
  StatusCode:
    description: "0=Startup 0; 1=Startup 1; 2=Startup 2; 3=Startup 3; 4=Startup 4; 5=Startup 5; 6=Startup 6; 7=Running; 8=Standby; 9=Boot loading; 10=Error"
    persist: true
    default: 7
    min: 0
    max: 10
  Ac/Energy/Forward:
    description: "kWh"
  Ac/Power:
    description: "W"
  Ac/L1/Current:
    description: "A"
  Ac/L1/Energy/Forward:
    description: "kWh"
  Ac/L1/Power:
    description: "W"
  Ac/L1/Voltage:
    description: "V"
  Ac/L2/Current:
    description: "A"
  Ac/L2/Energy/Forward:
    description: "kWh"
  Ac/L2/Power:
    description: "W"
  Ac/L2/Voltage:
    description: "V"
  Ac/L3/Current:
    description: "A"
  Ac/L3/Energy/Forward:
    description: "kWh"
  Ac/L3/Power:
    description: "W"
  Ac/L3/Voltage:
    description: "V"
  Ac/MaxPower:
    description: "W"
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Current state using this services.yml content:

[...]

pvinverter:
  CustomName:
    default: "PV Inverter MQTT"
    persist: true
  Position:
    description: "0=AC input 1; 1=AC output; 2=AC input 2"
    persist: true
    default: 0
    min: 0
    max: 2
  Role:
    default: "pvinverter"
  Ac/Energy/Forward:
    description: "kWh"
  Ac/Power:
    description: "W"
  Ac/MaxPower:
    description: "W"
  Ac/L1/Current:
    description: "A"
  Ac/L1/Energy/Forward:
    description: "kWh"
  Ac/L1/Power:
    description: "W"
  Ac/L1/Voltage:
    description: "V"
  Ac/L2/Current:
    description: "A"
  Ac/L2/Energy/Forward:
    description: "kWh"
  Ac/L2/Power:
    description: "W"
  Ac/L2/Voltage:
    description: "V"
  Ac/L3/Current:
    description: "A"
  Ac/L3/Energy/Forward:
    description: "kWh"
  Ac/L3/Power:
    description: "W"
  Ac/L3/Voltage:
    description: "V"

I had to manually set

W/xxx/pvinverter/2/Role {"value": "pvinverter"}

But the "Role" makes no difference on the next behavior.

1648588494657.pngRegistered device

1648588631644.pngBut not here shown

1648588699776.pngEM24 device has units

1648588805229.pngMQTT device has no units

1648588889590.pngEM24 has "setup page", MQTT not

1648589346779.pngEM24

1648589393329.pngMQTT

Over all it kind of works, but not as it should be (expected).

Next I will feed in some real data, will see what will happen.


What is "persist" in services.yml for?


1648588494657.png (14.9 KiB)
1648588631644.png (33.7 KiB)
1648588699776.png (22.1 KiB)
1648588805229.png (21.6 KiB)
1648588889590.png (17.8 KiB)
1648589346779.png (58.7 KiB)
1648589393329.png (60.3 KiB)
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image gone-sailing commented ·
Persist causes the values of that attribute to be saved in the dbus xml on the device so your settings are retained even after Venus device reboots. Custom Name has persist: true so that you don't have to reset your custom name every time you reboot your venus device.
0 Likes 0 ·
gone-sailing avatar image gone-sailing gone-sailing commented ·
I'm sorry I missed all your messages to me earlier. I don't get any email alerts from this forum. Your best option is to open an issue on GitHub and we can discuss this over on the GitHub issue.
0 Likes 0 ·
stundenblume avatar image stundenblume gone-sailing commented ·

No problem! I expected you on water (offline) for a view days :-)
Will open an issue.

0 Likes 0 ·
gone-sailing avatar image gone-sailing commented ·
It looks like you are missing one or two dbus settings that the PVInverter on DeviceInstance has, like phase config.
0 Likes 0 ·
stundenblume avatar image stundenblume gone-sailing commented ·
I started with the "minimal configuration" from the Victron documentation.

But I will try a full copy of the EM24 device.


0 Likes 0 ·
stundenblume avatar image
stundenblume answered ·

How Do I handle a reboot of venusOS?

After a reboot a existing temperature sensor was gone.

After sending the status massage to the driver again it worked normal. Is that the correct procedure?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image gone-sailing commented ·
Yes, that is the correct behaviour. Whenever you reconnect to the mqtt broker you should re-register with a status message. Dbus will ensure you pickup the same device instance you were allocated previously.
0 Likes 0 ·
gone-sailing avatar image
gone-sailing answered ·

I just published a new release v0.3.1 on github with better validation of the status message, a new DBus registration topic and some bug fixes.

https://github.com/freakent/dbus-mqtt-devices

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Thanks for you really nice software! :)

What is the proper way to update? just execute setup, or do I have the uninstall or remove something?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Just install the new version as per the instructions, but before rebooting just edit the /data/rc.local and remove the line that for the previous version.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

Just for future readers. It works with "pvinverter" and "grid" services.
If I have everything running I will write a howto in this forum and will post a link here.


Thanks @gone-sailing for this brilliant and extreme useful driver! It opens a world of until now unusable sources for sensors.

Edit:
I will close now this tab in my browser, I don't get any notifications if something happens here. So maybe a PM is necessary to get in contact.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

@stundenblume Thank's very much for the feedback. I have rolled your pvinverter changes into a v0.4.0 pre-release if you want to give it a try before I release a 0.4.1 more generally.

https://github.com/freakent/dbus-mqtt-devices

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

stundenblume avatar image
stundenblume answered ·

@gone-sailing
Ok, I will try it in the afternoon.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pau1phi11ips avatar image
pau1phi11ips answered ·

This looks amazing. I'd like to copy pvinverter data from one Venus install on a Pi in the garden across to the main Cerbo that has everything else attached to it.

I think this should be possible via Node Red? I have Node Red running on another Pi but I'm a total noob with it. I can see both installs in MQTT explorer fine.


I've ran through the Install and Setup notes on Github and now I'm thoroughly confused as to how to register the pvinverter on the Cerbo.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kotty avatar image
kotty answered ·

Hi @gone-sailing ,

thx for the nice software :) I'll try to implenet an oil sensor for oure home. This would run on an esp32 with deep_sleep and should only publish the remaining level all 12h. My mqtt code connects publishes messages and disconnects, but at disconnecting the device is removed from the function _remove_device, do you know a way to publish something that this would not happen at disconnect?


thx and regards

Kotty

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Hi Kotty, I’d need to see how you are using MQTT to be sure, but you must use the registration process each time your device starts. The dbus will remember your device and give you the the same Device Id. If you have any problems open a new issue on the GitHub repository. It’s easier to track there than on this forum.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kotty avatar image kotty commented ·

Okay, at the moment it is in development because some Sensors have not been arrived.

But i've copied many functions from your https://github.com/freakent/mqtt_wifi_sis because of missing time to write by my own.

0 Likes 0 ·
hsteinhaus avatar image
hsteinhaus answered ·

I have a smart grid meter (eHZ DD3) which has a D0 optical interface and provides high-res voltage, power and energy data once per second. A D0-compatible optical sensor is commercially available under the name "Hichi IR WiFi" for a very resonable price. The sensor contains an ESP8266_1M and is normally intended to run a Tasmota-based firmware, that supplies the readings to a MQTT broker.

Using this hardware, I have built a firmware using ESPHome, that supplies the data to the Cerbo running it's stock MQTT broker. The firmware is built to satisfy the expectations of dbus-mqtt-devices. After a few hours of coding, I am now able to see the readings of my D0 meter on my Cerbo (no battery and no Multiplus connected yet):

1678708330824.png

1678708006480.png

1678708057329.png

As D0/SML meters are very common here in Germany, maybe somebody else might find the ESPHome source code useful. I have put my work on Github: https://github.com/hsteinhaus/esph-gadgets/blob/master/esphome/d0-meter.yaml

@gone-sailing Thanks for publishing your driver - it was very helpful to get my meter data into the Cerbo!


1678708006480.png (72.3 KiB)
1678708330824.png (50.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

Awesome, I'm glad it was of use to you. It sounds like a good project.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

caspartfg avatar image
caspartfg answered ·

@gone-sailing thanks for this - just to say i've got it working on my boat now for temperature and pressure. My plan is to add more sensors now for the alternators, fridges and seawater. I also rebuilt the client to get it working on the WROOM-ESP32s I've got kicking around. After a bit of trial and error it's working now.... Great work, thank you!

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image gone-sailing commented ·
Thanks for the feedback, I’m glad it’s working for you.
0 Likes 0 ·
paul-kassenaar avatar image
paul-kassenaar answered ·

@gone-sailing
Dear Gone sailing,
I am really a complete newby but I really want to learn this.
I would like to display the weather forcast on my Cerbo GX.
For this I want to use the Openweather API with the GPS coordinates.
This gives back a JSON message that I would like to display. I understood that I will have to pubisch this JSON message on the DBUS.
I am completely lost where to start to figure out this further. I know how to grab data from the DBUS, but I have no idea how to get it there. MQQT, Node RED other method??
Would appriciate if you could give me some directions.
Sorry for the newby question.....


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

gone-sailing avatar image
gone-sailing answered ·

@paul-kassenaar

The GX devices are not general purpose displays, you can not just display any sort of data you wish. There are a list of devices types that VenusOS supports. Look up the docs for the Venus Modbus TCP interface. I’m pretty sure weather forecast is not on that list. This driver just simplifies using the same device types over MQTT. Sorry, you were probably expecting something more helpful.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paul-kassenaar avatar image
paul-kassenaar answered ·

@gone-sailing

Yes you are right I was hoping on more a direction where I could work on because I saw a project from Itsme ( https://community.victronenergy.com/questions/186357/add-a-data-field-to-a-dbus-device.html) were he somehow managed to get the city name with an API call in combination with the GPS coordinates I assume and displayed the cityname on the screen.

Anyhow thank you for the very quick reaction

Bye from Holland


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

paul-kassenaar avatar image
paul-kassenaar answered ·

Took some time but got it to work:

1698669495627.png


1698669495627.png (6.8 MiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jonofe avatar image jonofe commented ·
Would be great if you could share, how you solved this problem.
0 Likes 0 ·
paul-kassenaar avatar image paul-kassenaar jonofe commented ·
First I installed the MQTT to dbus driver

Than I used node red where i installed the Open weather Map node

Based on the GPS coordinates node I used the Openweathermap API.

I modified some of the Json output and made an MQTT call to the earlier installed driver.

I did modify the file gps.ini (in the directory drivers/dbus-mqtt-devices-0.7.5-beta/services) were I added the items I wanted to publish.

Than I got the data published on the dbus.

Next is with console command dbus-spy to check if the values are on the dbus.

Finally I did modify the gui and showed the data by editing the overviewHubEnhanced.qml file.

Did take me a long time to get it working but you can test every step.

Because I did not know how to program in node red and to work with payloads, messages, etc I did use a lot ChatGPT. The you can easely pull complete scripts.

Good luck

I

0 Likes 0 ·

Related Resources

Victron temperature sensor disambiguation table - which product supports which sensor