question

Enzo avatar image
Enzo asked

What is the total current of 3 outputs in parallel of a Phoenix Smart ip43 charger 24/25(3)

Hi,

Could someone please let me know what is the total current of 3 outputs in parallel of a Phoenix Smart ip43 charger 24/25(3)?

Would it be 25x3=75A? Is it still 25A total?

I am charging a single bank of 24V batteries and I can use all 3 outputs in parallel if this provides more charging current.

Thank you,

Enzo

charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Paul B avatar image
Paul B answered ·

still 25 in total, This is for one unit that has 3 outputs. I you have 3 units in parallel then the total would be 75A

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Enzo avatar image Enzo commented ·
Thank you Paul,

I could not see these parameters stated in any part of the manual.

Enzo

0 Likes 0 ·
Enzo avatar image Enzo Enzo commented ·
So, there is no use to connect the 3 outputs in parallel if one can provide the 25A total.


0 Likes 0 ·
Paul B avatar image Paul B Enzo commented ·
correct it will make no diferance
0 Likes 0 ·

Related Resources

Additional resources still need to be added for this topic