Multiplus 12 1600 70 short buzz on air con commpressor cut in
Brand new multiplus 12 1600 70. Running airconditioner new sparrow aircomader Mark 4 with Max watt of 950. When the airconditioner compressor cut in it draws about 70 amps inverter has a loud short low pitch buzz for about 1/8 of a second every time.
I seem to have missed your question?
You are running an AC from your multi, and it works?
David avatar image
David answered ·
That sounds like an overload from the AC in-rush current when its compressor first kicks in.
The AC may be a 950W unit, but on start-up it will draw considerbly more than the 1300W the 12/1600 Multiplus is rated at. As long as the in-rush is short duration (under 30 seconds and yours is under a second) and under 3000W (for the 12/1600), it should be fine, but get used to the buzz.
I had that on a 12/500 inverter and 12/800 MP when running a 230V fridge (pulling 37W running but 800W inrush)
Also occasionally get an overload note with the 12/1600 MP when the 230V fridge starts if I have the 800W Water Boiler on (but not noticed the buzz with this one - maybe too insulated from it to hear?)
Willem avatar image Willem commented ·
Is there by the way not a method to limit the inrush?
kevgermany avatar image kevgermany ♦♦ Willem commented ·
It would help if you open a separate thread with a full problem description.