Multiplus ii GX Modbus TCP Illegal Function ERROR

Hi

I have a Multiplus ii GX, and have been using the Modbus TCP function for a few months now without any issues. However a little over a week ago my read requests have been failing and I get a

Illegal Function ERROR. Now I know my unit ids and registers have stayed the same on the request side because I didn't update any code, and the Multiplus was not set to do auto updates. it's on v2.60.

Any ideas on why this would just stop working?

Thanks

Multiplus-IIModbus TCP
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image wkirby ♦♦ commented ·
Can you tell us which requests are failing? Unit ID and register?
0 Likes 0 ·
neil-swart avatar image neil-swart wkirby ♦♦ commented ·
All of them to be honest, but one example is ID 100 Register 817
0 Likes 0 ·
1 Answer
Mike Dorsett avatar image
Mike Dorsett answered ·

Illegal function Error on Modbus is usually caused by request function 3 instead of 4 or trying to write with the wrong function code. It may be possible that an update to the Modbus server has removed some flexibility - some servers give identical responses to read functions 3 & 4, some will give a function error as technically these sets of registers should be in different address spaces.