I have a victron 5000 quattro it has one hot, one neutral. As of now I have a Honda EU3000IS as back up for cloudy days to charge and help power my cabin. I want to upgrade to the EU7000IS, but only way to get full power is to use the plug with the two hot wires and one white going to the Quattro or I could only get 30 amps from the 120 plug. Do you offer a converter or is it possible to put both hot wires into the hot lead on the Quattro? Please help I am a little under powered when I have cloudy days and the EU7000IS would be a perfect backup if it would work with the Victron Quattro 48 volt unit.

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
ceriw avatar image
ceriw answered ·

Is your quattro 230V or 115V?

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ceriw avatar image ceriw commented ·

From the generator manual

1625845603916.png


If the switch is set on 120V only, all outputs are in parallel.


0 Likes 0 ·
1625845603916.png (21.3 KiB)
ejm avatar image ejm commented ·
it is 115V 48 volt system just one hot , but he EU7000IS has two hots to get full power. This is my dilemma
0 Likes 0 ·
ceriw avatar image ceriw ejm commented ·
when the switch on the generator is set to 120V only, the diagram in the user manual shows all outputs in parallel
0 Likes 0 ·
ejm avatar image ejm commented ·
115V
0 Likes 0 ·
ejm avatar image
ejm answered ·

i could only get 30 amps out of the 7000 watt generator if I use the 120v plug. to get full power I need the 4 prong with 2 hot wires

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejm avatar image
ejm answered ·

It will only pull 30 amps from the 120 side of the EU7000

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Kevin Windrem avatar image
Kevin Windrem answered ·

The limitation is in the generator: the 4-pin receptacle has a 30 amp breaker and only one half of that receptacle is active in the 120 volt mode. The "B" hot leg has no voltage on it in this mode.

You would need to run the generator in 240 volt mode then install a transformer to convert the 240 volt generator output to 120 volts.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ejm avatar image ejm commented ·
Great answer, Does Victron make the transformer? what is the model number i will order one
0 Likes 0 ·
Kevin Windrem avatar image Kevin Windrem ejm commented ·

Victron offers both autotransformers and isolation transformers. Either one would probably meet your needs.

https://www.victronenergy.com/upload/documents/Datasheet-Autotransformer-32A-and-100A-EN.pdf

https://www.victronenergy.com/isolation-transformers/isolation-transformers-2000va-3600va-7000va

The autotransformer is slightly less expensive. The isolation transformer provides automatic input voltage switching and complete input/output isolation which you may not need.

You'd need the 100 amp version of the autotransformer and the 7000 VA version of the isolation transformer.