question

ryancrist avatar image
ryancrist asked

Lynx Distributor ground and Smart Shunt Ground

Im doing a solar install where i have the Lynx Distributor and the BMV-712. My MPPT is a the 100/50 (ground wire connected to distributor). Do i need to make a ground connection to my chasis (travel trailer) from just the shunt, or both the shunt and the distributor?


Thanks!

Grounding
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
raphael avatar image
raphael answered ·

Since shunt and the negative distributor are on the same potential, it is enough to connect only the distributor or the shunt to ground.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic