Pheonix Inverter Wire Gauge Limitation vs. Peak Rated Power
The 500VA Pheonix VE.Direct Inverter is rated to support up to 900W of peak power, according to the datasheet. However, the maximum wire gauge that can the screw terminals can accommodate is apparently AWG8 (also according to the datasheet). If the inverter is running from a 12VDC power source and the power demand is surged to ~900W, then the inverter would pull over 80A (accounting for some efficiency loss) which is well above the ampacity of an AWG8 cable. This seems like a potentially dangerous situation, or am I missing something? Thank you
Geoff
inverter current draw
The inverter can supply the peak power only for a few seconds so I see no problem with the wire size.
Kevin Windrem avatar image
Kevin Windrem answered ·
But I agree, the peak power really isn't an issue for wire sizing. Use the maximum continuous power for wire size.
Marine wire has 105°C insulation. Marine 8 AWG will handle 80 amps continuous.