Good day all
Good day all
Looks like your genny isn't stable enough to provide a constant voltage..
Hi @offroadflow the generator runs the loads perfectly fine as well as charge the batteries with the Multi's disconnected
OK, then please tell me the exact V on the inverter input connections
Hi please see attached screenshots
Seems all good so far!
What is the interval time of the "switching bulk to passthrough"?
What exactly do you mean by "passthrough"?
At some times every 10-30 seconds.
On the Cerbo touch display screen, the Inverter indicates "Passthrough"
Please see attached