Multiplus II 48/5000 power dropping out with ESS system, AC PV and BYD batteries
Hi guys
I have a Multiplus 2 that seems to have intermittent power dropouts from time to time, the entire home load runs through the Multi so the customer certainly notices the dropouts. I can't see anything obvious in the monitoring aside from the VE.Bus state changing to OFF.
I have attached a sample day extract from VRM on the 7th December and highlighted the dropouts in red around 16:30.
Any help would be greatly appreciated.
Link to CSV - Click here
Multiplus-II
Is it possible to move the customers AC PV to the AC input, instead of the AC output?
I know that there are no DC MPPT chargers in the system, but please turn on feed-in excess DC in the ESS grid feed-in menu.
It looks like the DC voltage is creeping up as occasionally bits of excess power is fed into the batteries at 100% SOC, and then not allowed to reduce. So the battery voltage is creeping up over time.
In BYD batteries, over voltage situations can lead to eventual sudden shutdowns.
ross-skyenergy answered ·
Thanks for your reply @Guy Stewart (Victron Community Manager)
I have updated this setting below
The customer prefers the AC PV on the Output because they experieince frequent blackouts and at times have decided to turn the mains off all together and go off-grid.
Thanks again for your help, I will see how this goes.