question

derek-bristow avatar image
derek-bristow asked

Using K1/K2 relays on a 3-phase parallel Quattro installation

I have 6 x Quattro units in a 3-phase configuration. If I want to use the K1/K2 relays and Aux inputs can I use them on any unit - do they all behave the same way? I would assume that since the same configuration is loaded in each unit they would all be active?

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Margreet Leeftink (Victron Energy Staff) avatar image
Margreet Leeftink (Victron Energy Staff) answered ·

Each relay can be used for an individual function and can be programmed individually.

When programming the system, first sent the configuration to all units. Then afterwards go into the settings of each individual unit. Do this via “VE.Bus system configurator” and select the phase and then right click the Multi to go to its individual VE.Configure so each relay can be individually configured.

See this screenshot: 1605049580599.png


1605049580599.png (198.2 KiB)
2 |3000