Hi Folks,
I have installed a MultiPlus Compact in my camper set up, it's all working fine on 12v but when I connect shore power, the RCD on the shore power supply trips within a couple of seconds. When I disconnected the Earths from the PE input/output everything works as it should and nothing trips.
I have the body of the unit earthed to the body of the van. I have tried it with the incoming earth from shore power earthed to the van and not earthed to the van, but this doesn't seem to make any difference.
Do I need to change the settings of the relay?
Any help appreciated.
Is the RCD tripping immediately or after a few seconds when the Multi pass through the shore?
What happens if you disconnect the AC OUT?
wayneh avatar image
wayneh answered ·
@matthias Lange - DE
It trips immediately after it passes through through the shore. Just to add, I am building out the system so right now there is nothing connected to the system, I have the AC out going into a breaker on the consumer unit within the vehicle but that breaker is switched off.
wayneh avatar image
wayneh answered ·
I have figured it out. The guy who installed the 240 side suggested that we run the shore power through a trip on the way in as a safeguard rather than assuming the campsite power/trip was safe. What I didn't realise was that he wired the incoming neutral and earth into the common buzz bars that the AC out was wired to. I have now isolated the incoming neutral and earth and all is working fine.