Hi, I installed a Venus GX to monitor a solar system, it works very well and I found the problem... the customer was sucking -80amps @ 50v (yes 4kw !) using the system to make tea and toast at the same time !
The system overloaded and shutdown (funny that !) so it was maybe only at 4kw for 10-15 seconds.
The strange thing is... a few hours later I logged in and the -80amps was clearly depicted on the V/A graph, clear as day and a pleasure to see.
But when I go back in to show the customer the logging, the particular -80amps plot is not there anymore, all of the days data is there, I am familiar with logging software I have triple checked the dates, times etc, I have stretched out the data to the hour that it was covered in, I have downloaded and reviewed the xls file,
But there are no xls timing gaps, there are no graphical gaps, it is like the software has 'smoothed' the 10-15 seconds of -80amps down to a more consistent -10amps for that time of the day.
How I wish I had taken a screenshot.... and now I'm even questioning did I really see it !
NB the shutdown was an Outback Inverter so there is no Victron error log, likewise no low battery alerts as none were set.
Appreciate any comments.
Venus OS
oropi avatar image
oropi answered ·
For the future I have set some alert rules, being Discharge Current Low which I have set to -60 amps (minus 60 amps) and because it was mandatory I set the Discharge Current High Reset after reaching -40amps.
I also had to set a Discharge Current High (mandatory) so I set alert at +120amps which is above the solar capacity, so I shouldn't receive any high current alerts.
The next step is "Notify After " which I have set to 60 seconds, but does this mean notify me if the state remains at more than -60amps for over 60 seconds and also does not reach -40 amps within 60 seconds.
So in event of an 20 second Inverter (non Victron model) overload when it hits -60 amps and the inverter shuts down, and because the sun is shining the solar current rises to say +20 amps into the battery, do I not get an alert ?
oropi avatar image
oropi answered ·
The more I look into it the more conundrums I see in trying to use using the Discharge Current Limit as an Inverter (Non Victron model) overload or shutdown alert.
For instance if the solar was producing 60+ amps and the inverter was overloaded with 80amps, then the net is -20amps for 20 seconds, before swinging to +60amps (solar input) which will not trigger a DCL alert.
So what using one of the Venus GX inputs as a state monitor ?
The inverter is on 24/7 and if the inverter shuts down a relay closes and puts a state change across one of the Venus inputs to register a state change on the appropriate widget ?
Teun Lassche avatar image
Teun Lassche answered ·
@Oropi Lead VRM developer here.
We do not change the sent data in any way. We do keep the number of points in a graph limited, so if you look at a larger time range, the graph is smoothed a little. You can still look up any spike in the data by zooming in.
I just checked your specific case and when you zoom in around Sunday 2 August 2020 05:37:00 UTC, you clearly see the spike you mention: