2x 48/5000 multi s in parallel,gx bmv712

Is there a way of settting gen start for entering the night time period with fully charged battery? As well as set for overload and low battery ?

Generator
3 comments
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Yes,

You could program the relay at your GX, in several logics

I have programmed for low soc and overload, but I want to programme for if day hasn’t charged batteries upto 100 percent for gen to kick in and top up , so system hits night fully charged , am I missing another setting? I wondered about something off of relay on mppt example day/ night lighting...

Harold avatar image Harold Matt drummond bell ·

May be you can use the testrun setting, but it will then run dayly.
In the Assistants programming I don't see any time related setting.

1 Answer
Justin Cook - Bay Marine Supply USA avatar image

@Matt drummond bell what about using the "periodic test run" feature, set daily, with a start time, and just set to "run until battery is fully charged"?

https://www.victronenergy.com/live/ccgx:generator_start_stop