question

Atte Varis avatar image
Atte Varis asked

100/50 MPPT Trends Solar Voltage 38v-15v

Hi,

I'm not sure if this is supposed to do this or not. My MPPT 100/50 Solar Voltage is jumping between 38v and 15v continously in same pattern. Even tho if I check solar voltage with multimeter it's staying at same voltage. Picture below, is this normal?

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ยท

Hi @Atte Varis,

That is not normal, and usually indicates at poor electrical connection at some point between the PV panel and the MPPT.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Atte Varis avatar image Atte Varis commented ยท

Thanks @Guy Stewart (Victron Community Manager), Have to check those connections then.

0 Likes 0 ยท