Can a Lynx Ion + Shunt be used as disconnect for non-Victron batteries?

(Both Power In's in this photo are configured so positive terminals are fused. MultiPlus configured as Parallel 120VAC. All devices are connected to VenusOS running on a RaspberryPi.)

Can I install a Lynx Ion + Shunt to use as an emergency battery disconnect even though I don't own Victron batteries? I can't tell from the documentation if Victron batteries are required. I also don't see a way to wire it for a remote switch for the main relay.


What I'm trying to accomplish is a physical external battery disconnect for Emergency Services. By turning this this switch to the off (open) position I want to disconnect the battery bank. And turn off the MPPT controllers if possible.


Being able to also use the BMV-712 to turn the main relay on and off would be ideal. This appears to be the only Victron device that might allow me to use it like a Battery Protect, but also allow charging from the MultiPlus'.


Thanks in advance!

dc system
powerdist.jpg (108.3 KiB)
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
victron@flagg.org avatar image
victron@flagg.org answered ·

Does this connect/disconnect non-Victron batteries? I’m still unclear if the device has a switch to do that, or only uses software to tell batteries to turn off.

Being able to use this as an automatic safety disconnect switch for high/low voltage like I was able to with the battery protect would be with the price of admission for me. (The MultiPlus has killed the BP option in this system)

The remote switch I was thinking of mounting emergency services is an open or close circuit in a remote weather proof enclosure outside the structure. At least that’s how I’ve wired the MPPT and Battery Protect circuit in the past.

Is there documentation some place that explains how the remote on/off works? There are other types of switches that may function the way I would like it to. Blue Sea has rocker switches that press on and off for their remote switches and indicate their state.

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

WKirby avatar image
WKirby answered ·

Although the Lynx Ion has a remote switch terminal, it's not going to work for emergency purposes.
This is because it is push to turn on and push to turn off with the same contact. This could mean that, by activating the emergency switch, a fireman could turn the system on if it is already off.