question

ehsab avatar image
ehsab asked

Bypass mode?

Hi,

Is there a bypass mode to activate when one would like to externally bypass the inverter (Quattro) for example when to service units ?

My Eaton UPS has this mode when i shall bypass it, it helps me switchover without downtime.


Kind Regards

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Tom avatar image
Tom answered ยท

Yes you use your Mk3 and turn off both inverting and charging. This way you can just use your plugged in shore power or generator.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ehsab avatar image ehsab commented ยท

I don't think you understand the question, i would like to switch the current to not flow via the quattro at all.

0 Likes 0 ยท
Tom avatar image
Tom answered ยท

I think you would need to install an external transfer switch to do that. It is less costly to turn off charging and inverting or run a second AC out 2 that bypasses the quatro inverting .

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ehsab avatar image ehsab commented ยท

Yes i will install an external switch.

0 Likes 0 ยท