deft-electrical avatar image
deft-electrical asked
MPPT 100/20 wont switch off load at setpoint
Hello. I setup manual high and low voltage set points to turn the load output off to my fridge for testing. The voltage can go well below the setpoint for any period of time (over 2 minutes) and it will remain on. It does work by forcing it with always on or always off. This will not be ok for lithium batteries.
MPPT Controllers
Did you removed the jumper from the VE.direct port at the bottom? This jumper will overrule the settings via the app.
deft-electrical avatar image deft-electrical commented ·
Thanks! This worked! The odd thing is all the other settings I fiddled with appeared to work besides the load output settings.
Matthias Lange - DE avatar image Matthias Lange - DE ♦ deft-electrical commented ·
The jumper is only for the behavior of the load output and it is described in the manual.
So instead to blame Victron for a bad customer service you might just read the manual first. Victron don't have a end-user support. In this forum are end-users helping each other it's not directly for end-user <-> Victron communication.
https://www.victronenergy.com/support
ejrossouw avatar image
ejrossouw answered ·
Hello @Deft electrical
Firstly, this is not a Victron support website and you should follow the formal channel if you require support. Can you please elaborate a bit more on the full system configuration as without knowing battery type, inverter, ESS., if firmware is up to date etc, you will struggle to get a response. Have you tried a forum search as well?