Bosvark avatar image
Fronius and quattro on different phases
Hi all,
Some guidance please
In a 3 phase system (220V L-N) i want to use two 8.2kW Fronius Primo inverters on L2 and L3. Then on L1 a 10kVA Quattro with DC coupled PV.
My question is on the GX setup to show both fronius inverters, what are the location options in the GX as the fronius inverters are on different phases than the quattro.
Thanks
Fronius
Hi @Bosvark
This should work just fine, you can select on what phases the PV inverters are installed.
You do need an energy meter (ET340) to measure the loads on all phases for a complete overview.
4 comments Share
The et340 is rated for 65A. What three phase Meter is recommended for above 65A maximum 100A?
Hi @Bosvark
You can use the Carlo Gavazzi EM24DINAV53DISX, see this page: https://www.victronenergy.com/live/energy-meters:start
This meter uses CT’s for measurements above 65A / phase
Hi Daniel
If using SMA or SolarEdge PV inverters there is no zero feed-in support from the GX. Does this mean that the PV inverters has their own energy meters installed and does zero feed-in separate from the GX?
Hi @Bosvark
I don't know how this works with other brands than Fronius.