question

thijs avatar image

MultiPlus-II 48/5000/70 continuous overload shutdown

MultiPlus-II 48/5000/70 is shutting down continuously with an overload error after some issues on the grid network.

Batteries are full and the external grid is off (as the mains circuit breaker failed). BlueSolar Charger MPPT 150/70 is connected and providing power (as the sun is up...)

Now the MultiPlus keeps trying to start up, but fails within a couple of seconds with an overload error. However, the circuit breaker towards the load is off as well, so there literally cannot be any load on the inverter at all.

Is this a bricked MultiPlus or is something else going on?

Tried a lot of stuff, including restarting the system through the Color Control GX as well as with the on/off button itself.

Anything else to try?

The system is installed in the south of France, and I'm asking for someone else, so troubleshooting is going to be a pain.





Multiplus-IIerror
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

6 Answers
Menno47 avatar image

Dealer replaced the MultiPlus II. After reinstallation the setup works correctly. But up to now Victron could not tell me what caused the problem and so I am still worried that it might breakdown again.

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Eujean Hugo avatar image

I am also concerned - we now have 2 MultiPlus II units - both 3kVa with the overload issue - even with no or very little load present.

The 1 unit up to the point where it goes to overload within a few seconds of starting up - and cant be used at all. The other goes to overload alarm 1 or 2 times a day - with very little load - then error goes away and it keeps going like normal - but I guess it will also fail completely soon.

The number of overload (with no actual overload present) issues reported by clients and installers is a serious concern.

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Zak avatar image

Hi Thijs,

Just discovering now your initial message, have you solved you problem ?

I also have the Multi 2 48/5000 with CCGX and batteries.

Regards


Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Menno47 avatar image

Hi Guy Steward,

are there special reasons known for this breakdown? I had no problems for two months and the only reason I can think of was a peak demand of 6 kW yesterday around 10 am. Is this a possible cause?

2 comments Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

This can be a reason for the failure.

Try what Guy wrote. If this doesn't solve the problem, you have to start a RMA.

A 6kW load is well within the spec of that inverter. Without knowing exactly what happened then, it is difficult to say what is leading to the issue now.

I first assume that there is an issue external to the unit, bad connection or short somewhere, however once the unit itself is isolated from EVERYTHING ELSE, and if it persists, then something has gone wrong inside.

If you contact your dealer/installer, they can help.

Guy Stewart (Victron Community Manager) avatar image

Hi @thijs,

Please physically disconnect and remove all cables and connections to the Multi except the battery, which you have tested as acceptable voltage at the Multi's battery connection terminals.

If the issue persists, it must be a fault and please get in touch with your installer/dealer, or fill out this form.

Share
10 |3000 characters needed characters left characters exceeded

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Martin Coetzee avatar image

My MP2 was Faulty, it did the same. Was only a few months old.