AC Current sensor giving the wrong value

I have a 3-phase ESS-system with an AC-coupled PV-system.

I am using 3 AC current sensors ( https://www.victronenergy.com/meters-and-sensors/ac-current-sensor), connected to the temp-inputs on the Multiplus'es to show the values from the PV-system.

The problem is that my Victron system gives me way to high values.

In this very moment, my PV-inverter is producing 14200W, but according to Victron its about 21200W.

How can I calibrate this?

skarmbild-2024-05-04-111629.png

Multiplus-IIAC PV Coupling
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
duivert avatar image
duivert answered ·

There is the problem, manuals says 1,2,3 on for 7kw not 4 :)

img-6344.jpeg


img-6344.jpeg (207.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duivert avatar image
duivert answered ·

Are they setup right? Dipswitches set right? Wired right?

There normally are not very accurate/slow but this is a bit to much

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Pontus Lindberg avatar image Pontus Lindberg commented ·

I hope so. The dipswitches are all set to 7kW (no. 4 on, rest off) as my total solar is about 20kW.


Wiring should be correct aswell.

I havent really found any other settings for these, are there?

0 Likes 0 ·
Pontus Lindberg avatar image
Pontus Lindberg answered ·

Yes! That was it. I missunderstood this image and had it set up the exact opposite :)

image1.jpg


image1.jpg (16.3 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duivert avatar image duivert commented ·
Yes its a misleading image :), glad its solved!