question

jleverf avatar image
jleverf asked

Pulsing lights, Unstable Voltage, 3 phase x Quattro 10kVA (When inverting, no other supply)



Hi All,

I've run into an issue I've never seen before, hoping someone on here might have some insight!

As per the video below, we are having sporadic pulsing of lights at the site where our installation is. In the video at approx 40 seconds, the lights start pulsing at around 1Hz.







There are about 10 huts on the site, in addition to ~10 outside lights in the central area. Standing in the middle area, different groups of huts will be pulsing at random times, and the outside lighting will also pulse at random times. From what I've gathered, the set of huts that are pulsing at any given time are likely all tied to the same phase, and therefore being driven by some issue in the given inverter at that point in time.


I spent an entire day isolating different sections of the site and disconnecting any potentially troublesome loads (water boilers, ice makers etc.), and as far as I've seen, the issue persists with random load combinations. I.e. switch off one half of the site, the issue is there. Switch off that half and switch on the other half, the issue is there again.

We have quite a few similar installations with the same type of loads and we haven't seen this issue before, so I'm leaning towards this being a system issue rather than a load issue.


The system is as follows:

  • 3 Phase: 1 x 10kVA Quattro per phase
  • 66kVA genset on AC1 in, nothing on AC2
  • 3 x 8.2k Fronius Primo
  • 40kWh Powerplus LiFe4833P 48V

Notes on the Solar System:

Based on previous posts I'd seen, I thought it might be an issue with the Fronius Inverters, however, I shut down and isolated all the solar and the issue persisted. I also deleted the PV assistant to see if this was causing interference, but this had no effect and the issue persisted.

When the solar was shut down/isolated, and the PV assistant deleted, from the perspective of the Victron system the PV side of the system effectively didn't exist, and the issue persisted, so I'm quite confident this is not where the issue is coming from.

Notes on the Genset:

When the genset is running, the issue stops. The issue is only evident when the system is running on the inverters alone.

Notes on the Inverters:

The issue begins when the genset turns off and the system begins operating from the inverters/batteries alone.

For context:

  • The system is operating well within its capacity/not being overloaded. During operational hours, the average power per phase is about 2-5kW. The issue appears to happen both in cases where a phase is lightly loaded and where a phase is medium loaded.

1713149177587.png


The big irregularity that I'm seeing is that the output voltage is highly unstable! As can be seen below, the voltage jumps all over the place between 225V and 250V, and in outlier cases, can drop to ~200V, or up to 256V.


This issue is making it very difficult for people to work on-site so a solution is quite urgent and our distributor appears to be out of ideas at the moment.

If anyone has come across a similar issue in the past, your insight would be greatly appreciated!

Please let me know if anything needs further clarification,

Best Regards,

Jethro

voltagequattro 10kva
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
h2009 avatar image
h2009 answered ·

Can I recommend isolation by turning off all breakers that are not the lights.

I have a similar issue with my house, pulsing lights but it’s definitely because of one device in my setup. The device has a technology called power pulse, but even with that drivable it still occurs as the loads kick in/out.


it might be in your situation that there’s more than one device.


failing that, check your neutral lines maybe a common loose cable.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jleverf avatar image jleverf commented ·
Thanks for getting back to me h2009!


I've done a fair amount of troubleshooting of the loads, it's a pretty simple site so there's not much there of concern. There's only really a couple of lunch huts and offices. There's still a chance that it's a load issue, but we have a fair few installations powering pretty much identical equipment and I haven't come across this issue as of yet.


All power cables are torqued to spec during manufacturing and are supposed to be checked during installation, however, I'll be sure to double-check. This would be an ideal outcome if it was the issue!

0 Likes 0 ·
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @jleverf


The first thing I would think of with the low voltage state getting to 200V is that the inverters are hanging on to an AC input for too long. Adjust the AC input voltage acceptance limit to increase the minimum AC input voltage higher, say 215V for example. I don't think that's related to the core issue at hand, but still a good idea.


You've isolated the most common cause of flickering which is the AC PV. This is most common when the AC PV production is equal to the AC load, and the Quattros and Fronius are 'hunting' between idle and inverting (which they do by raising the voltage slightly), which leads to shifting of the voltage around. But I will rule that out for further troubleshooting for now as you are saying that it's already been isolated.


The next step, which is annoying but necessary, is to physically switch the units so that they are driving different phases.


This will help to isolate the issue between a physical hardware problem inside one of the Quattros, or some interaction between any arbitrary Quattro with the site wiring.


If the lights continue to pulse on phase 1 after physically connecting the Quattro from phase 2 to the phase 1 AC wiring, then it's far less likely to be a physical hardware issue, and far more likely to be something else (a bad connection or some other interference).

If switching the units resolves the issue, it hopefully solves your immediate problem. I could still be a wiring issue, that was resolved when re-wiring, or an issue inside the Quattro itself. It doesn't necessarily arise to the level of a replacement, report back with the results.


Be aware of all the safety implications on this sort of procedure, I am not sure what kind of loads you're running, but make sure everything is programmed correctly so that the correct phase sync is maintained if that is necessary.


Also agree with the comment above that the neutrals should all be checked around the site (depending how you isolated your loads in your other troubleshooting, this might not have isolated a loose or neutral wiring issue).

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image
Alexandra answered ·

@jleverf

Besides the suggestions by @Guy Stewart (Victron Community Manager) and @h2009 ...

The thing I see there is it is not inverting only? I see grid feedback. It can only do that when connected to grid. So synchronised to grid voltages.

LED lights with some of the cheaper power supplies don't like anything but 220v to 235v. So related to voltages definitely.

If you switch off the input breaker does it stop? That is true inverting where the system gets to decide for itself what to do instead of synchronization. They system should output 230v per phase when physically disconnected from grid. If not. Dig deeper.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

Why is ask if grid is connected i see feedback... So very likely that is what is related to the flicker? Are you using the ESS assistant? LOM detection?

1000035142.jpg

0 Likes 0 ·
1000035142.jpg (214.0 KiB)
Guy Stewart (Victron Community Manager) avatar image Guy Stewart (Victron Community Manager) ♦♦ Alexandra ♦ commented ·
That could also be the AC PV connected to the AC output feeding power back into the batteries for charging.


I am presuming this site is off grid.

0 Likes 0 ·
jleverf avatar image jleverf Guy Stewart (Victron Community Manager) ♦♦ commented ·
Hi,


I was just about to comment this. Yes the system is fully off-grid.

These snapshots were taken from the last week, so the PV inverters are online. This will show negative output power when they are charging the batteries.

When troubleshooting the issue, all the PV and genset were locked-out so just the inverters were able to supply site power.

0 Likes 0 ·
jleverf avatar image
jleverf answered ·

@Guy Stewart (Victron Community Manager) - Posting here as I couldn't post as a comment at this time.

Hi Guy, thanks for getting back to me! Apologies for the essay, I'm just trying to provide as much context as possible. Please see my comments below.

AC Input Voltage ~215V:

  • We previously had this set as standard at 215V, however it was causing issues in installations with Quattro's installed. We found that with some load transitions on the genset, the volts would tank down below 215. The inverters would follow it the genset down to 215, then reject it for an undervoltage when it dropped under and try and carry the load themselves. Since they were working in power assist, they couldn't carry the load, and so they tripped on overload.
  • From what I've seen there appears to be a difference in the recovery of Quattro's vs. Multiplus II.
  • With the Multiplus', if this happens, and then the load is dropped down to a non-overload level, the inverters will come back online and recommence powering the load.
  • With the Quattro's, they appear to seize up when they go into a fault state, and the load needs to be dropped and all inverters reset (with the switch) for them to come back online. This would happen in the genset undervoltage case, and site power couldn't be restored until the inverters were reset manually.
  • By allowing the inverters to ride through the transition, they could keep the genset online and maintain power.

AC PV:

  • We haven't come across this specific case yet, but we were having a similar case where we needed to have the genset running to handle peaks, but the batteries were at 100%. The load was bouncing around the input current limit, so the inverters were constantly jumping between charge and discharge which seemed to be making the lights flicker.
  • So far I've only been able to solve this manually by reducing the input current limit during these times so the inverters have to discharge a little (~1kW/phase). I'm considering trying to automate this with node-red when I find some time, with something like: when SOC>95%; input current = 0.8 x output current; until SOC<80%, but that's work for the future!

The next step, which is annoying but necessary, is to physically switch the units so that they are driving different phases.

  • I was thinking that it could be a hardware issue with the master, that was potentially shifting downstream to the remote units.
    • Do you know what data is passed by the master? I.e. do the remote units try to track the master voltage, or does the master just send a delayed firing signal for the remote's FETs?
  • On this point, there are no three-phase loads on site, would it be possible to just re-program the units to shift the master across?
    • Noting that the AC Input and Fronius Inverters would be locked-out when doing this, so it would only be the inverters driving the loads.
  • As another possibility, since they are all single-phase loads, would it be possible to shut down 2 inverters and reprogram the remaining one as single-phase to see if the problem persists in isolation? If this is possible, I could cycle through each inverter to see if this isolated the issue.

If the lights continue to pulse on phase 1 after physically connecting the Quattro from phase 2 to the phase 1 AC wiring, then it's far less likely to be a physical hardware issue, and far more likely to be something else (a bad connection or some other interference).

  • Just a note on this point: the pulsing appears to be happening on all phases but at different times. For instance, Lunch Room 1 will be pulsing for ~1min, then everything might be stable for ~5 mins, then Lunch Room 3 will be pulsing for ~1min. I didn't manage to get a load-phase map, but I had the feeling this was phase-related as it was switching between random huts at different times. I've got high hopes this is the case, because if huts on the same phase are pulsing like this at different times, there's a chance the site is possessed by a ghost.


If switching the units resolves the issue, it hopefully solves your immediate problem. I could still be a wiring issue, that was resolved when re-wiring, or an issue inside the Quattro itself. It doesn't necessarily arise to the level of a replacement, report back with the results.

  • Physically switching the inverters might be quite difficult under the site conditions. In trying to avoid this, I'd hope a solution might be too:
    1. Get our tech to re-torque all power cabling, specific attention provided to the neutrals.
    2. Ask site to double-check/re-torque all their neutral connections.
    3. Reprogram/shift the master inverter across and run the inverters in isolation to see if this delivers the desired solution.
      1. Test whether the issue is with the master.
    4. If 3 fails to provide any insight, run each inverter as a single-phase in isolation.
      1. Verify each inverter works in isolation.


Be aware of all the safety implications on this sort of procedure, I am not sure what kind of loads you're running, but make sure everything is programmed correctly so that the correct phase sync is maintained if that is necessary.

  • There shouldn't be any issue on this point as site loads are very simple and no three-phase loads. Ideally, when this work is being done there will be no one on site anyhow.


3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

I didn't realise that this light issue was happening on all 3 phases.

I would try switch masters and seeing if that has any impact, that should be fairly quick as it's only a software change.

If that doesn't work, your suggestion to reprogram the units as single phase and then run them individually is the next better test.

Understood this means you can't use the AC input and AC PV, that is a good thing for our troubleshooting process.

I agree with everything else you've said.

There was another suggestion by a colleague that there could be some inductive interference issue from the light tube drivers. I presume that all the lights that are having issues are the same type, and driven by the same drivers. Could you confirm that?

There are drop in replacement LED tubes for fluro tubes, which use a different type of starter electronics. Would it be possible to replace one of the troublesome tubes with one of the LEDs and seeing if that makes any difference for that light.


Regarding the 215V situation, understandable, but at that point it's really not a Victron centric issue that the voltage is sagging so low in those conditions, the generator voltage needs to be raised/stabilised. Getting down to 200V is not a good situation, even though it's less immediately painful than an overload blackout.

There should be no difference in behaviour between Quattro and MultiPlus in overload. For a simple overload both should recover automatically after 30 seconds, and then give 3 attempts before requiring a physical switch intervention. Do you have a VRM site where this has occurred so I could have a look at the error log?

0 Likes 0 ·
jleverf avatar image jleverf Guy Stewart (Victron Community Manager) ♦♦ commented ·

Thanks for the feedback! I'll devise a test plan for testing the changed master and individual inverter operation.

All the site huts are from a large equipment rental company so they should have the same lights. However, the site electricians would have installed the outside area lights, so there's a chance these are different. It's worth noting the customer/project is quite sustainable-focused so I'd imagine the lights they installed are LED already. It's a pretty easy fix so I'll look into testing with an alternate/LED version.


Completely agree with trying to avoid the low-voltage situation, definitely needs further investigation on our part down the track.

The relevant testing was quite some time ago and thankfully we haven't had any overload instances on site in recent month's so I don't have any direct data on hand, however, I'll be heading out to test a new unit next week that uses Quattro's, so I'll see if I can replicate. That said, from memory during testing, I directly switched out Quattro's for Multi's to test and saw different behaviour. I've seen the three-attempt thing mentioned but haven't been able to replicate in practice, they always seem to lock out on the first go. I'll get back to you with results / the VRM site when I'm testing the unit next week.


Thanks for the help so far, I'll get the team out to implement these troubleshooting steps and let you know how it goes. Hopefully, this lets us isolate the issue!

0 Likes 0 ·
Good luck, appreciate the good attitude in approaching this. Looking forward to hearing results.
1 Like 1 ·