juergen pflug avatar image
juergen pflug asked
VenusGX ModBus TCP register addresses correct?
Hi.
I am trying to interface the VenusGX via Modbus TCP.
I have downloaded the CCGX-Modbus-TCP-register-list.xlsx as provided via the download link by email from Victron.
Date downloaded: 2019-08-25
According to the excel table "Document versions" it is: "Rev 23"
I have then tried to connect to the VenusGX using ModbusView 1.61 from Ocean Controls.
After some frustrating time playing around I get first results!
But I have a problem with the provided addresses in the excel sheet.
For example "Serial(System) address should be: "800"
but I have to use address "801" in ModbusView to get the expected result!
Is that something that ModbusView does wrong or is the address table wrong?
...or what am I missing here?
Thanks for helping
Modbus TCP
juergen pflug answered ·
I forgot, Venus GX Firmware version = v2.33
Rob Howdle avatar image
Rob Howdle answered ·
Hi Juergen,
You will probably find this a lot when using Modbus. Typically, Modbus numbers its address registers starting at 1 (so the bits in a 16-bit integer would be 1-16). Most other (PLC) type equipment, would usually number from 0 (so bits 0-15 in the previous example). So you basically need to apply an offset (n + 1) whae addressing integers and bits!
Hope this helps.
Rob
Just an update...
I am now using QModMaster which is free and without limitations!!
You can get it from here:
http://sourceforge.net/projects/qmodmaster
Since then, all port numbers seem to be correctly assigned.
and I managed to read out all my attached devices via the Venus GX ( Smart MPPT & Quattro inverter)
Best regards
Jürgen
Just an update:
I am now using QModMaster and the ports number all seem to be correct. ( No + 1 needed )
QModMaster is free and has NO limitations!
You can download it from here: