voltimus avatar image
voltimus asked
Multiplus II 5000 48v not charging full amps
I have 3x MultiPlus-II 48/5000/70-50 with 3 LFP batteries 18S x280Ah and PV inverter AC coupled.
I was getting battery charge at over 10kW, but after I installed Cerbo GX updates now I'm getting only 6kW charge no matter what i do. Inverter settings are 70A charger, Cerbo GX > ESS >"limit charge = off". Inverters are located in room with 16-18C room temperature and just slightly warm.
Any ideas why it is behaving so? and how to debug this issue?
Multiplus-II
nickdb avatar image
nickdb answered ·
What is the battery CCL that it is sending to the GX? Have you set a current or Voltage limit in DVCC?
(You also don't seem to have followed the Factor 1 rule for PV inverters)
voltimus avatar image voltimus commented ·
CCL -150A for every battery. battery BMS is not talking to Cerbo GX.
DVCC is OFF (BMS on every battery )
No, PV inverter will not push more than 15kW to MPII (export limit is set and additional smart meter is installed just before MPII)
The thing is that just some time ago i saw charger charging 10kW+ , but not it is capped ~6kW
Alexandra avatar image Alexandra ♦ voltimus commented ·
If you have battery life on switch it off.
voltimus answered ·
I have "Optimized without BatteryLife" ON