tobuildings avatar image
tobuildings asked
ESS recharge battery instead of discharge
I have a ESS with 3 Multiplus II 5000VA, Cerbo, MPPT, 50kWH Battery LiFePo
Today I updated the BMS and wanted to do a full battery cycle. Up to 100%, down to 0% and up again.
Loading was easy. I set "keep battery full".
Afterwards I set "Optimized without BatteryLife" min SoC 0%
After hitting 12% the ESS started charging with 50A. - cerbo did not show any BMS alarm like "low voltage"...
In VRM Portal it says "recharge"
Now it is at 31% and still wants to charge from grid, I set max. charge current to 1A for now.
I dont know how to stop the "recharge" - tried to switch trough different ESS modes, set min SoC to several different values - still no difference.
I want the battery to dicharge for know, but I dont know how to make it... AC loads I have, but battery charges with 1A from grid.
ESSSOC
matt1309 avatar image
matt1309 answered ·
Hi @ToBuildings
My guess is the BMS is requesting the recharging. Any data/settings visible within the BMS that gives a hint?
4 comments
The BMS can't make the system charge the battery, it merely sets limits for charge/discharge and/or blocks the battery being used if it leaves its specs.
There are multiple settings that could cause a system to behave like this, ESS SOC minima is only one of them.
There are voltage limits in the inverter setup, cut-offs and other thresholds in the assistant.
Supported batteries take this into account in their config docs, most likely the peripheral settings around ESS are incorrect. If this is a non-supported battery, best to consult with the supplier for the config it requires.
matt1309 avatar image matt1309 nickdb ♦♦ commented ·
@nickdb Under normal conditions yes, but if the BMS minimum limits change when already below said limit the victron system would charge the battery to that limit.
nickdb avatar image nickdb ♦♦ matt1309 commented ·
I suggest you re-read the original post.
It would not apply to that scenario, unless other thresholds are hit.
If BMS min voltage was hit, the victron system charges to sustain level doesn't it?
I assumed that would mean that BMS min voltage had changed as part of the update given no mention of any other settings being updated.
I see your point that maybe the sustain is set too high but root cause is surely BMS given no mention of any other changes before the behaviour occurred.
thanar avatar image
thanar answered ·
Strange. Even if the battery had hit an inverter-set low-voltage limit and had to "sustain", you should definitely see some feedback in VRM / Console. Any chance your ESS assistant was setup with a different battery? Did you check the ESS settings, through VEconfigure?
Funny thing is I did the same to my battery today, because BMS-reported % was way off, and the procedure you mentioned worked as expected. Battery discharged down to 1%, stayed there for a few hours, and updated to 0% as soon as the BMS cut off. The inverter entered "sustain" mode, I limited the charge current through DVCC until it went out of sustain and adjusting minimum SoC since.
What is ESS training video
ESS Quick Installation Guide
ESS design and installation manual