question

t3mschm2d avatar image
t3mschm2d asked

EVCS - Ground fault - Where to find some docs about the error

Hey Victron-Commuity,

currently I've installed a EVCS-NS as described in the Victron manual. The wallbox is connected to all three phases and I have also connected an RCD ahead of it as prescribed. After commissioning, however, I get the current status "Ground fault". Unfortunately, I have not found any documentation on the status message itself and had hoped that I could get some help here. Do you know how I can solve this?

Best regards from Germany!
Tim

Groundingevcs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Lucian Popescu (Victron Energy Staff) avatar image
Lucian Popescu (Victron Energy Staff) answered ·

Hi Tim, most of the time, when there is a ground fault reported by the EVCS, that's truth.

Can you measure the voltages between L1 and GND, L1 and N, N and GND and share them here?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

t3mschm2d avatar image t3mschm2d commented ·
Hi Lucian,

sorry for the late response. I've remeasured between all phases, restarted the Wallbox and the error disappeared. I'm a bit clueless why this error happened, but it's gone for now and the wb is running absolutely fine for around 1,5 months.

@Stefan Boldt I hope you were able to fix your problem as I can't give you any information about how mine fixed itself :D

0 Likes 0 ·
Stefan Boldt avatar image
Stefan Boldt answered ·

Hi. Same problem hier. Between L1 and GND and L1 and N I have exactly the same voltage (232V) Between GND and N I have 0,14V.

I my case the error message "Ground fault" shows only for a short time. Mostly less then a minute. I only know this, because I monitor it. It gows from 0 - Disconnected to 8 - ground fault and back to 0 - Disconnected in less then a minute.

My Wallbox is connected on the grid side.

Any Ideas?

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

I think you have a different problem. From time to time you have a ground fault error, his unit is not functional because it detects all the time missing ground.
In your case, I think I know what the problem is, please send me an email with the VRM portal ID.

0 Likes 0 ·
Stefan Boldt avatar image Stefan Boldt Lucian Popescu (Victron Energy Staff) ♦♦ commented ·

Thanks. Where can I find/see your email address?

0 Likes 0 ·
Lucian Popescu (Victron Energy Staff) avatar image Lucian Popescu (Victron Energy Staff) ♦♦ Stefan Boldt commented ·
If you click on my name here, you don't see it?

If not, lpopescu@victronenergy.com

0 Likes 0 ·
Stefan Boldt avatar image Stefan Boldt Lucian Popescu (Victron Energy Staff) ♦♦ commented ·

Thanks. Will send you the data. But.. If I click on your name I get this page:

https://community.victronenergy.com/users/1959/lucian-popescu.html

But somehow I can't find any email address.

0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ Stefan Boldt commented ·
It's in the message text. Lucien has selflessly exposed himself to the world's spammers for you.
0 Likes 0 ·
Lucian Popescu (Victron Energy Staff) avatar image Lucian Popescu (Victron Energy Staff) ♦♦ kevgermany ♦♦ commented ·

It's ok, my email address is displayed in so many places :) like in the link below

https://www.victronenergy.com/contact

0 Likes 0 ·
Stefan Boldt avatar image Stefan Boldt Lucian Popescu (Victron Energy Staff) ♦♦ commented ·
Thanks Lucian for your support. The Firmware Upgrade resolved the sporadic Ground Fault errors on my Wallbox.
0 Likes 0 ·
Lucian Popescu (Victron Energy Staff) avatar image Lucian Popescu (Victron Energy Staff) ♦♦ Stefan Boldt commented ·
Thanks Stefan! When the official version will be released, make sure you're updating it, now it's a beta.
1 Like 1 ·
Stefan Boldt avatar image
Stefan Boldt answered ·

@t3mschm2d I got a beta firmware from Victron which fixed the problem with the Ground fault issue.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Related Resources

Additional resources still need to be added for this topic

Ground, earth and electrical safety


Additional resources still need to be added for this topic