Per query above, I'm trying to size a generator. Options are 2200w or 3200w 230v units. What current can I get at 12-13v?
For those when it's not clear.
I misread 12-13V. Which is -1V.It's a range so do two calcs, one with 12V, one with 13V.
Do not overload a Generator by running it on its rated power. The Generator will wear off in lightspeed.
If you have a Generator with 2200W continious power, the load should not exceed 2/3, hence 1450W.
This mean, your charger should not have more then 100A charging output @12V.