Can I use 30amp shore power on Multiplus-ii 12v 3000 120amp

Hi

I have a 30amp fused shore power already installed in my van. Can I use this with the Multiplus-ii? Or do I have to swap my shore power to 50amp? I purchased the Multiplus-ii already because i got a really good deal on it. I'm hoping there's a setting I can change or it will run fine with the 30amp.

I'm not planning on having a heavy load on the system, maybe a small microwave at most and a laptop.

400ah of battery

This is my first van and experience with this equipment.

thanks


Multiplus-IIshorepower
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

There is a setting for the input current limit.

Please read the manual.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

snoobler avatar image
snoobler answered ·

Assuming you're in North America:


30A shore is 120VAC single phase.

50A shore is 120/240VAC split phase.


Most victrons sold in the states are 120VAC only. They do not make a split phase model, but they make a 2x120 model that intelligently manages switching back and forth between 30A and 50A shore power supplying power to both legs of a 50A RV AC panel. I'm assuming you have the pure single phase model. In that case you MUST only supply 120V to the unit. An adapter to plug 30A RV power cable into 50A shore only pulls from one 120V leg, so you're good there.


There are two important values:

1) AC input limit - the maximum amount you can draw from shore and not trip input breakers.

2) Battery charge current - maximum charge current sent to the battery.

Must remember that the two currents are NOT at the same voltage. 30A input current limit is 30A * 120V = 3600W. 3600W / 12V = 300A of battery charging current.

Also important to understand the AC input current limit is for BOTH charging AND passing through AC to any loads you're using, i.e., loads + charging. The unit will manage the charge current to stay under the AC input limit, but if your loads exceed the AC input limit, you can trip the breaker UNLESS you have PowerAssist enabled where the inverter will draw from batteries and boost AC output to meet the loads in excess of the AC input current limit.

For a 400Ah battery, you likely want to limit it to 40-80A charging for longevity.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blueu avatar image blueu commented ·
thank you very much!
0 Likes 0 ·
wiresnotfires avatar image wiresnotfires commented ·
If they did have the 2x120 model, would it then be better to wire a 50A breaker and inlet into their system instead of 30A?
0 Likes 0 ·
Kevin Windrem avatar image Kevin Windrem wiresnotfires commented ·
If the load distribution panel is rated for 30 amps and has a single 120 volt input, then upgrading the shore power connection will add 20 amps of charger/load capability. Replacing the load distribution panel with a split-phase input and moving some loads to the second leg would enable more devices to run off of SHORE power. But remember that the 120x2 Multi is a single 120 volt 3000 VA inverter so when running off of the inverter (no shore power), loads would still be limited to 2400 watts (20 amps).
1 Like 1 ·
Kevin Windrem avatar image
Kevin Windrem answered ·

No reason to upgrade your shore power connection. The 3000 VA Multi produces 2400 watts while inverting or about 20 amps @ 120 volts. Charging is 120 amps or about 14 amps at 120 volts from shore power.

Set the input current limit to 30 amps and the Multi will adjust charging current so that the combined charger draw and AC loads will remain under 30 amps.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

blueu avatar image blueu commented ·
thanks!
0 Likes 0 ·

Related Resources

MultiPlus-II Product page 

MultiPlus-II Manual

MultiPlus-II 230V Datasheet 

VE.Bus Error codes

Additional resources still need to be added for this topic