question

luphi avatar image
luphi asked

EVCS automatic switching between 1p and 3p

In https://community.victronenergy.com/questions/215013/single-phase-charging-on-three-phase-setup.html

@Lucian Popescu (Victron Energy Staff) describes a not officially supported method to make that work with the existing EVCS models. On the hardware side, the 4p contactor has to be replaced by 2x2p contactors. 1st contactor for P1 and N, 2nd contactor for P2 and P3. The 2nd contactor will be switched by the 2nd relay, which is not in use in the original setup.

These contactors might work: https://www.se.com/de/de/product/A9C20842/installationssch%C3%BCtz-ict-40a-2s-220-240v-50hz/ They are a bit wider, but should fit. Probably the DIN rail needs to be extended.

On software side, the modbus register 5056 hat to be set to 2

But before I'm going to invest in the contactors (btw, street prices are far below the list price), I wanted to play with the modbus register, to see, how the EVCS behaves. The documentation says, range is 0-2 and default is 1. But when I read it, the value is 65535 and I'm not able to change it.

$ mbpoll -1 -0 -a1 -r5055 -c2 evcs
mbpoll 1.0-0 - FieldTalk(tm) Modbus(R) Master Simulator
Copyright © 2015-2019 Pascal JEAN, https://github.com/epsilonrt/mbpoll
This program comes with ABSOLUTELY NO WARRANTY.
This is free software, and you are welcome to redistribute it
under certain conditions; type 'mbpoll -w' for details.

Protocol configuration: Modbus TCP
Slave configuration...: address = [1]
                        start reference = 5055, count = 2
Communication.........: 172.23.1.15, port 502, t/o 1.00 s, poll rate 1000 ms
Data type.............: 16-bit register, output (holding) register table

-- Polling slave 1...
[5055]:     65535 (-1)
[5056]:     65535 (-1)

Can please anyone confirm or proof me wrong.

Cheers... luphi


evcs
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

18 Answers
hbraak avatar image
hbraak answered ·

technical it seems to be the same inside


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Lucian Popescu (Victron Energy Staff) avatar image
Lucian Popescu (Victron Energy Staff) answered ·

You can change it

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

luphi avatar image
luphi answered ·

Hello @Lucian Popescu (Victron Energy Staff), thank you (again) for your quick response, but I can't change it. When I try, it says "Written 1 references" but when I poll again the value stays unchanged.

By the way, other registers like 5017 (max current) are working fine.

$ mbpoll -0 -1 -a1 -r5056 evcs 2
mbpoll 1.0-0 - FieldTalk(tm) Modbus(R) Master Simulator
Copyright © 2015-2019 Pascal JEAN, https://github.com/epsilonrt/mbpoll
This program comes with ABSOLUTELY NO WARRANTY.
This is free software, and you are welcome to redistribute it
under certain conditions; type 'mbpoll -w' for details.

Protocol configuration: Modbus TCP
Slave configuration...: address = [1]
                        start reference = 5056, count = 1
Communication.........: evcs, port 502, t/o 1.00 s, poll rate 1000 ms
Data type.............: 16-bit register, output (holding) register table

Written 1 references.
$ mbpoll -0 -1 -a1 -r5055 -c5 evcs
mbpoll 1.0-0 - FieldTalk(tm) Modbus(R) Master Simulator
Copyright © 2015-2019 Pascal JEAN, https://github.com/epsilonrt/mbpoll
This program comes with ABSOLUTELY NO WARRANTY.
This is free software, and you are welcome to redistribute it
under certain conditions; type 'mbpoll -w' for details.

Protocol configuration: Modbus TCP
Slave configuration...: address = [1]
                        start reference = 5055, count = 5
Communication.........: evcs, port 502, t/o 1.00 s, poll rate 1000 ms
Data type.............: 16-bit register, output (holding) register table

-- Polling slave 1...
[5055]: 65535 (-1)
[5056]: 65535 (-1)
[5057]: 65535 (-1)
[5058]: 65535 (-1)
[5059]: 65535 (-1)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

luphi avatar image
luphi answered ·

nobody with any ideas? Any help is really appreciated.

Cheers... luphi

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

It should work, I have just tested
0 Likes 0 ·
luphi avatar image luphi Lucian Popescu (Victron Energy Staff) ♦♦ commented ·

Thank you for double checking. So, what am I doing wrong? Do you use a different modbus tool to change them? Since I can change other registers, I don't believe, it's a tool issue. Have you had the same default values 65535? I only have these values for the 5 registers, listed above.

Sorry for all the questions, but still can't make it work.

0 Likes 0 ·
Lucian Popescu (Victron Energy Staff) avatar image
Lucian Popescu (Victron Energy Staff) answered ·

can you give me the vrm portal ID?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

luphi avatar image luphi commented ·

send by email

0 Likes 0 ·
luphi avatar image
luphi answered ·

Hello Lucian, thank you for your help. it's working now.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kds avatar image
kds answered ·

Did you install the contactors finally ?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

luphi avatar image
luphi answered ·

Yes, I did. In theory everything should work. I'm really exited to test it out. Unfortunately the car is not yet delivered. The dealer promised he will get it next week....

What I was missing, was modbus register 5100, which enables/disables phase switching. Setting it to 1 makes the registers 5055-5059 changeable.

From hardware perspective, I was indeed going for the contactors mentioned above. (less than 40€ per contactor including shipping in Germany). I had a DIN rail laying around, so I replaced it too, to fit the size of the new contactors.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jochenku avatar image jochenku commented ·
Thank you for the heads-up on this modification, I'm strongly interested in doing it, too, now that solar excess is slowly becoming available again.


Might you be willing to share the exact specifications or even a link to the newly installed contactors/relays? That would be great...


Thanks a ton and best regards,

Jochen

0 Likes 0 ·
hbraak avatar image
hbraak answered ·

I impleteted the phase switching for the EVCS NS and made a tiny documentation. Comments are appreciated!

BR

Heiko


EVCS_Phasenumschaltung.pdf


5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Nice :)
0 Likes 0 ·
kudos50 avatar image kudos50 commented ·
Very nice ! Was planning on opening it up soonish to figure things out. Having this is way better :-)
0 Likes 0 ·
Just one mention, remember that it is a feature still in beta. And it is not supported yet
1 Like 1 ·
hias0815 avatar image hias0815 commented ·
Any updates/Results of testing with enough sun?

Is it working as expected?

Regards

Matthias


0 Likes 0 ·
chinook avatar image chinook hias0815 commented ·

Hi hias0815,

I have the first Version of the EVCS, with the actual Software installed. I have 6-9kW from 7am to 2pm and I have never seen switching the System it self from 1 to 3 phase. (Auto Mode 1/3ph, Manual Mode 3ph). When i start in Manual Mode and switch then to Automatic Mode, sometimes automatic mode is running 3ph. Maybe I have to change the parameters, like in the comments below, because my BMW i3 is only charging with max. 16A per phase.


What i also see, if the EVCS is active, the DVCC max. charging current is not regarded by my System. When my Symo Converter has more Solar Power available than the EVCS is consuming in 1ph mode, all the MPPT450/200 power is charging the battery. This happens only if the EVCS is active. When my car is not connected Battery charging is limited to the DVCC max. current.


Regards


Korbinian


0 Likes 0 ·
19andy89 avatar image
19andy89 answered ·

Hello

That's good news

Does the switching of the phases work automatically?

or does the switchover have to be done via Modbus?

Does the car also accept the switch?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hbraak avatar image
hbraak answered ·

Up to now, I tested only the manual mode.

When I switch the Manual Mode via Modbus 5055 from 1 to 0(three phase) during charging the EVCS stops charging, switches to 3-Phase an starts again within a couple of seconds (Parameter 5101 might be the corresponding).

Sun is missing...also next days here in cologne. Testing the auto mode seems to take a while.

May be Lucian can give an explanation to the parameter 5057 - 59 in the Modbus TCP Register List?

Best Regards

Heiko

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

webblaster avatar image webblaster commented ·
Hello Heiko,

any further experience with the mod?

Greetings from Lindenthal

Felix

0 Likes 0 ·
hbraak avatar image hbraak webblaster commented ·
works pretty good, parameters I attached below the last post.
0 Likes 0 ·
luphi avatar image
luphi answered ·

they build the switching hysteresis, I assume:

- switching from 1p to 3p if surplus >(5057)W for (5059)s

- switching from 3p to 1p if surplus <(5058)W for (5059)s

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hbraak avatar image hbraak commented ·
Thanks!
0 Likes 0 ·
luphi avatar image
luphi answered ·

To be honest, I'm not sure, if it is really correct, what I wrote.

I configured 5059 to 10s and 5057 to 4500W. The EVCS is charging since a couple of minutes now with 16A@1p and ~2kW are send to the grid, but it's not switching to 3p :-(

My assumption was, that the EVCS sums up the current charge current + the energy send to the grid and if that is bigger than the value of register 5057, it would switch to 3p. Unfortunately that doesn't happen. Does it really requires 4500W (4800W by default) in addition to the ~3600W 1p charging to switch to 3p?

@Lucian Popescu (Victron Energy Staff) would you mind to clue us up.

Cheers, luphi

1713971166136.png


1713971166136.png (122.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

hbraak avatar image
hbraak answered ·

screenshot-2024-04-28-202254.pngHere are my parameters for phase switching. Ich works pretty good. My E-UP only can charge via two phases.

BR

Heiko



5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

luphi avatar image luphi commented ·
Thanks for sharing.

Does that mean, I should multiply your values by 1.5 ?


0 Likes 0 ·
hbraak avatar image hbraak luphi commented ·

Hi, it depends on your hardwaresetting. What is your max. current per phase? And what is your EV capable to charge, on how many phases? Can you provide some more info?

BR Heiko

From your previous post is looks like you have max current of 16A per phase (take care of your circuit breaker!) So if your EVCS should switch to 3 Phase mode, you have to take a value for 5057 below 3800W.

If your EV charges at 3 Phases the minimum Power would be 6A * 240V * 3 = 4320W or 2880W for 2 Phases. In the first case I don't know how the set the 5058 parameter, that it would make sense, only if you have a setup for 32A max... For the second case as it is for my e-up the 5058 should be 3800W>(5058)W>2880W. I took 3200.


May be this helps.


0 Likes 0 ·
luphi avatar image luphi hbraak commented ·

cables and breaker cover 32A

The car (EV6) can charge up to 16A at 1p or 3p, means I have a gap between ~3700W (16A@1p) and ~4200W (6A@3p).

Cheers, luphi



0 Likes 0 ·
hbraak avatar image hbraak luphi commented ·

I think so...


but, considering this information:

https://ev-database.org/de/pkw/1471/Kia-EV6-GT#charge-table

1715170005836.png


It should be possible to go to 32 A for the vehicle. If your cables to the WB ist capable to transport 32A and your circuit breaker is for 32A, then you can got to 32A with the EVCS an your gap should disappear.

BR

Heiko

0 Likes 0 ·
1715170005836.png (144.6 KiB)
chinook avatar image chinook hbraak commented ·

Hi hbraak,


thank's for your great description and explanations. I updated my parameters now and i will test it the next day's (my car is limited to 16A/ph, i set 5057 to 3700W and 5058 to 3500W). What i don't understand, why are these parameters depending on the vehicle charging power and not on the available solar power?

Do you have an idea?


Regards

Korbinian

0 Likes 0 ·
jonaspv avatar image
jonaspv answered ·

The Discription for modify the charger is for the new generation without a display, does it also work with old Version, whitch has the display?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jochenku avatar image
jochenku answered ·

Hi everyone!

I just completed the modification of my EVCS according to the 'instructions' of @hbraak in this topic. Thanks a ton!

At first glance everything is looking good and after changing ModBus register 5100 fro 0 to 1 I see the modified SETTINGS menu where it is possible to preselect 1P/3P for MANUAL and AUTO mode.

But how does SCHEDULED mode behave? 1P? 3P? Any parameters that i overlooked?

Best regards, Jochen

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jochenku avatar image
jochenku answered ·

@Lucian Popescu (Victron Energy Staff) Maybe any ideas how SCHEDULED mode works? 1P or 3P?

10 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi, no, the 1P/3P mode is not supported, was added just for tests, in preparation for EVCS V2
0 Likes 0 ·
jochenku avatar image jochenku Lucian Popescu (Victron Energy Staff) ♦♦ commented ·
@Lucian Popescu (Victron Energy Staff)


Thanks for the quick reply but obviously my question was not clear enough. Another try:

With the second relais installed and register 5100 set to '1' will the EVCS charge with 3,7kW (1P) or with 11kW (3P) when scheduled mode is selected and 16A is set in the active scene?

Thanks and best regards, Jochen

0 Likes 0 ·
jochenku avatar image jochenku jochenku commented ·

@Lucian Popescu (Victron Energy Staff)


May I kindly push this question again, it's been a couple of days...

The reason for my insistence is that I cannot really test it out during the summer when I use only PV surplus power to charge the EV.

During the winter I use scheduled charging 3P/11kW with flexible energy prices during the night and depending on if after this modification the EVCS scheduled mode uses 1P or 3P or both I may need to work on a software solution in order to guarantee 3P charging during the night.

Thank you...

0 Likes 0 ·
Hi, sorry, but 3P/1P is not yet a supported feature. SO I can't give you any response about it. But there are few users here using that feature, maybe they can give you some help.
0 Likes 0 ·
jochenku avatar image jochenku Lucian Popescu (Victron Energy Staff) ♦♦ commented ·
Sorry, I thought that would be a rather easy question. But no problem, I will try it myself and report back...
0 Likes 0 ·
It's an easy one indeed, but once I start doing this, I'll have to do it again and again. I hope you understand, sorry!
0 Likes 0 ·
jochenku avatar image jochenku Lucian Popescu (Victron Energy Staff) ♦♦ commented ·
In the meantime I found the answer to my question: scheduled mode with 16A as charging current did only charge using 1P last night. :-(


Unfortunately that is quite disappointing, as I use scheduled mode to charge the EV quickly during the night with 11 kW using low energy prices.

@Lucian Popescu (Victron Energy Staff) Is this intentional? This way the whole modification loses it's appeal for me...

0 Likes 0 ·
The logic for 1p/3p switching will be checked and updated when this will become a supported feature. For now, it's just a test in preparation for the next hardware revision.
0 Likes 0 ·
ahtih avatar image ahtih jochenku commented ·
I have Auto mode running as 1p/3p and Manual/Scheduled 3p just fine.
0 Likes 0 ·
jochenku avatar image jochenku ahtih commented ·

Thank you @AhtiH that is the solution! After changing the "Manual mode phase" selection from 1Phase to 3Phase the scheduled charge worked at 11 kW last night.

That means the labeling in the menu is not clear enough, as the selector for MANUAL mode also controls SCHEDULED mode.

1719979867609.png

So I kindly suggest to rename it accordingly, eg. "Manual / scheduled mode phase". Would have saved me quite some time / hassle.

And a bit disappointing that Lucian was unable to give that information despite the fact that I've asking multiple times which parameter controls the number of phases the scheduled mode uses.

Anyway, problem solved in 'community style'...

0 Likes 0 ·
1719979867609.png (214.7 KiB)
jochenku avatar image
jochenku answered ·

Today I had the chance to observe and test the phase switching for the first time. Good news is it works, but...

I started today's test with a current limit of 16A and parameters #5057 = 4400 and #5058 = 3500. The charger remained at 3.6kW 1P for appr. 30 minutes. As soon as I changed #5057 = 3400 (and #5058 = 3200) it switched to 3P right away (appr. 11:45)...

1719326780451.png

So let's first agree how the control algorithm seems to works. The parameters 5057 / 5058 are not solar excess, but the actual EV charging power that the EV uses at the moment to charge the EV.

So how does AUTO mode calcualte the charging power used? Let's see the EVCS manual, section 2.2 Features (my markup):

1719325263506.png

So AUTO mode will try to keep feed-in at 0, of course within it's limits (min - max charging current). That means, there might be a small issue for

  1. installations which only provide a limited amount of solar excess during the preferred charging times either because other consumers require power during charging or because solar power itself is limited to an effective power below appr. 4.5 - 5.0 kW.

    and / or

  2. installations that are limited to a max charging current of 16A (due to regulatory, power management, charging cable or other reasons).

    Because 16A single phase (considering 230V as reference voltage) equals 3.68 kW charging power and because the minimum current is set at 6A either 1P or 3P (per most EV's specification) this means for three phase operation the minimum power will be 4.14 kW.

So there is a gap between 3.68 kW (max single phase) and 4.14 kW (min three phase). But in order to achieve (and mantain!) a switchover from 1P to 3P the charger would have to reach >= 4.14 kW power which it will never do 1P with a 16A limit.

Setting the limit to 18A (regulatory issues aside and proper wiring and fusing assumed) would result in a gap of 0W as 18A * 230V = 3 * 6A * 230V = 4.14 kW. This might work but will be far from ideal because there is no room for any kind of hysteresis.

My understanding as of now is, that in order to benefit from the AUTO phase switching

  • the car has to be able to charge single phase with minimum min 20A (for switch to 1P to 3P, 2P is better but rare as layed out further above)
  • the EV charging cable must be able to allow min 20A
  • wiring and fusing must be compatible with 20A ops.

So for the sake of science ;-) I will swap my EVCS main fuse from 16A to 20A, set the current limit to 20A and the parameters 5057 to 4600 an 5058 to 4200. This should give the EVCS 400W to play with.

I will report back...

Best regards, Jochen


1719325263506.png (165.3 KiB)
1719326780451.png (275.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.