Hemang Shah asked

MultiPlus-II 2x 120V vs MultiPlus-II

Hi all,

I have a 30amp shore power sail boat. I understand that the MultiPlus-II 2x 120V is for 50amp L1 & L2 shore power connections.

Could I use the MultiPlus-II 2x 120V even for a 30amp shore power connection? Any advantages / disadvantages? or should I just get the MultiPlus-II 24/3000/70-50 (for 24v)

Thanks

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
derrick thomas avatar image
derrick thomas answered ·

The 2x120 can be used in a single phase 30 amp system without issue. If you have future plans to upgrade your boat to 50 amps I would go ahead with the 2x120. If not, save a few bucks and stick with the single 120.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

thamilto1r avatar image thamilto1r commented ·
Does the Multiplus II 2x120 require a configuration change to accept the 30 amp shore power or does it adjust automatically? Same question for 20 amp shore power.
0 Likes 0 ·
derrick thomas avatar image derrick thomas thamilto1r commented ·
It will handle it automatically but you should set the incoming ac current limit accordingly.