alacrity avatar image
alacrity asked
MultiPlus voltage fluctuations
MultiPlus 2KVA 120V with remote control panel.
Installed this past spring; everything worked fine for four months. I was out of the country for three weeks; when I got back to the boat and turned the inverter on it was only providing 102V AC (previously it was about 120-122). As soon as I supply a load it starts wildly fluctuating between 80V and 128V. Any significant load trips the overload.
Connecting to shore power or running the generator both work fine.
Any possibility I can reset the inverter somehow?
Multiplus-II
Alexandra avatar image
Alexandra answered ·
@Alacrity
First port of call is an ac wiring and connection check.
(But more thorough would be a whole system check).
Settings don't change, what does change is the physical install.
How are your batteries?
alacrity answered ·
Batteries are good; can run everything (fridge, freezer, electronics, etc.) except the inverter.
I don't know how the wiring could have suddenly gone bad, but I will check that next.
alacrity answered ·
Measured the voltages at the connections on the Multiplus:
DC input is 13.6v.
AC output is 102v with no load. Any load causes the wild fluctuation in AC voltage output.