Multiplus- grid backfeed?

I've purchased, but haven't installed, a Multiplus 24/2000 to connect to my pv system.

I'm concerned that it'll backfeed the grid and have read there's a setting which when changed will allow backfeeding the grid.

Is there a way to prevent it from backfeeding the grid even though the "mains" has no power? (LOM)


Thank you

MultiPlus Quattro Inverter Charger
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
elvis avatar image
elvis answered ·

LOM is there to prevent exactly that.

No mains, No feed in.


Anyway, unless you install the ESS assistant backfeeding cannot be selected.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

pda1 avatar image
pda1 answered ·

That's good. Is LOM a setting? If it is then is there an internal relay which will completely disconnect AC wires that might be able to back feed?


I think I found the answer and hope this applies the Multiplus-


2.1 What is LOM detection?

LOM is an automatic process that detects a loss of the mains/network/grid supply. After the detection, the inverter/charger will open its back-feed relay, making sure there is no live AC voltage on its AC-inputs, and anything connected to these inputs.


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

derrick thomas avatar image
derrick thomas answered ·

Unless you plan on using ESS, back feeding is not even a possibility. Even with ESS back feeding can be disabled.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

danqcca avatar image
danqcca answered ·

if you do not enable ESS, you cannot feed in. 2 print screen from the ESS configuration.
Even if you enable ESS, you can restrict feed in to the grid / to the AC IN

nofeedin.png

possiblefeedin.png

By default, your Multiplus will not feed in to the grid. Don't worry, be happy and connect it.


nofeedin.png (42.4 KiB)
possiblefeedin.png (75.8 KiB)