fordens asked

3.5kWh load on Multiplus ll 12/3000?

Hi all,

I try to figure out if a constant load around 3.2kWh-3.5kWh will be an overkill for Multiplus ll 12/3000? Any ideas if this will damage the unit?

Thanks for help

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

You mean kW?

Considering it can deliver 2400W and will derate if this is sustained, or operated in warmer temps, the unit is horribly undersized. Get a 5kVA instead and preferably a 24 or 48V variant .

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fordens avatar image
fordens answered ·

That will require a complete change of the battery bank which I would like to avoid off course

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nickdb avatar image nickdb ♦♦ commented ·
Indeed but options are limited with larger inverters mainly because at those loads and 12V you’re pulling around 300A.
0 Likes 0 ·
taylortops avatar image taylortops nickdb ♦♦ commented ·
I know I wouldn’t feel comfortable running that amount of current
0 Likes 0 ·
Michelle Konzack avatar image Michelle Konzack taylortops commented ·
If i already think on what wires you have to use that the Inverter get AT LEAST 10V...


Recommended Cable lenght under 1m and at least a H01N2-D 70mm2 which support 341A S1. A H07Z-K with 70mm2 support only 270A AFAIK.