solar-tech avatar image
solar-tech asked
Victron MPPT - Max Charge Voltage ?
Hi Everyone,
With MK Deka Gel batteries the manufacturer states a max charge voltage of 14.58V on a 12V block.
With a Victron MPPT, if we enable temp compensation - then the controller could exceed this in very cold conditions.
If we don't enable temp compensation then the batteries won't get as well charged in cold conditions.
I can't understand why there isn't a max charge voltage on the temp comp settings ?
Thanks,
Mark.
MPPT Controllers
kevgermany avatar image
kevgermany answered ·
Because max charge voltage changes with temperature. Your maker is giving a max at standard temp. Set absorption voltage (max charge voltage) as per instructions and enable compensation.
solar-tech avatar image solar-tech commented ·
Hi, thanks for your reply. No, this is the absolute max voltage at 15 deg C... as per their tech note (and confirmed with their tech staff in the USA) :
klim8skeptic avatar image
klim8skeptic answered ·
@Solar Tech you have to use the temp compensation figures that Deka provides.
It looks like it is -18mv/C for a 12v battery @ 25c. Do check those figures.
solar-tech answered ·
Yes, I have.... those figures are for 15 Deg C with a co-efficient of 0.003 Mv / cell / deg C .... as per their document below (and confirmed with their tech staff in the USA), which equates to 14.58V (2.43 vpc).
I quote Deka : "Continuing to temp. comp below 15°C the change voltage will be above our max. charge voltage recommendation."
"and so a voltage limit should really be set ? Correct. Max. Charge voltage should be set to 14.58V (2.43 vpc)"
See highlighted text:
@Solar Tech the next sentence specifically says that temp compensation is to be applied to battery temp under 25c, and batt temp over 25c.
solar-tech avatar image solar-tech klim8skeptic ♦ commented ·
Yes... from 25 deg C down to 15 deg C. At that point it should stop.
And in a hot climate the minimum charge voltage is at 35 Deg C. (both highlighted).