martydee avatar image
martydee asked
Multiplus 12/1600/70
IMG_0616.jpegMultiplus is going to overload at just above 400w
This is on a hairdryer/toaster/ hot air gun
It’s worked fine for over 1 year
Battery is a Roamer 300ah 250a battery
It has been getting lower on output showing overload started at 1000w
With the inverter input connected directly to the battery and the output connected directly to a variable inductive load (heat gun); at circa 400w load, the output voltage drops to 170vac while the input remains above 13vdc.
Now I’ve sent the inverter back and they have said it’s all fine
Im at a loss
Multiplus-II
mvas avatar image mvas commented ·
Are you sure the heat gun is an inductive load?
martydee avatar image martydee mvas commented ·
Tbh I’d be unsure
But it’s doing to same toaster/ heat gun (variable load ) and curling tongs
Toaster and curling tongs rated 750-800 w
It has got progressively worse ie toaster would have toasted fully before overloading
To barely able to switch on
In the picture the voltage drops to 173v
mvas avatar image
mvas answered ·
Look at the AC amps!
Watts does not equal volts x amps.
Highly inductive?
What is the volts x amps for the toaster ?
That should be purely resistive.
martydee answered ·
Ac amps are low (why?)
Toaster is a 800w can’t find amp details
But they all worked fine and still do on ehu