Can you explain me what exactly is the "BoostFactor"?
Thank you
Kind regards
Pablo
Hello Victron Team,
Can you explain me what exactly is the "BoostFactor"?
Thank you
Kind regards
Pablo
Hi Botnic, please use the help function in VEConfigure. Its the go to place for all these kind of questions.
Hi, so a quick case study question.
We have a system with Quattro 8k/230V with input current limit set on 60A and Power Assist Boost ratio is set to 2.0.
How let's assume we have an abrupt load request - Quattro assumes 2.0*60A current (according to the manual). And at that moment what does it exactly do?
1. Would it prepare those 120A from the batteries? If such, does it ease the input for a few cycles and inverts power from the battery?
2. Would it keep 60A from the input and add 60A from the batteries?
The below chart shows currents active and reactive and THD (sorry for LQ graph, hope it's readable) on the input of Quattro (actually output from grid inverter). It looks like when power assist kicks in, it eases the input for a "second", adds power from DC and brings input current to a previous state.
It's worth mentioning it's not happening always, but at times, which is strange.
I think this is related to your other question.
However, it is normally recommended to be at 2.0. It is the peak power that the inverter will provide when shore current is no enough.
So, for normal operation, it is recommended to be set to 2.0. Does this mean that if my AC current limit is set to 9 amps that it would provide up to 18 amps?
Also, What scenarios could arise where this value would be better set to another value either higher or lower?
Boost Power Ratio to be expected, if the inverter has to assist. WKirby was faster. :o)